Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-11 Thread Roger Price
On Wed, 11 Jan 2017, Merk - Oliver wrote: nas4free: /# more /usr/local/bin/upssched-cmd #!/bin/sh I would strongly recommend specifying which script interpreter is to be used: dash, bash, csh, ksh, ... For example #!/bin/bash There seem to be too many case statements in this script.

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-11 Thread Merk - Oliver
Thanks for your help. I have posted information, but I think I have answered myself, so maybe you haven't got an info. Sorry, using a mailing list is new for me ;-) Let's forget about the QNAP problem. It seems that although upsc is getting correct status information ("OL", "OB", "OB LB", OB

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-11 Thread Merk - Oliver
I've setup nas4free (latest version 11.0.0.4, which has NUT 2.7.4) in a VM and configured it via webinterface to my APC UPS and set "shutdown mode" to "UPS goes on battery" with a timer of 30s. Then I started runtime calibration on the UPS and after 30s nas4free has shut down! I think this is

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-10 Thread Merk - Oliver
In the meantime I learn more and more about NUT. And I've learned that QNAP is not using all of NUT but has instead of upsmon its own process called upsutil (https://qnap.uservoice.com/forums/213378-enterprise-features/suggestions/4225398-full-and-native-support-of-nut-ups-management) which is

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-09 Thread Charles Lepple
On Jan 9, 2017, at 9:46 AM, Merk - Oliver wrote: > > I then connected to my QNAP and set the UPS settings on the web interface to > "Shutdown server if power loss is 5 min", the UPS is configured to an > SNMP-Connection with its IP-address. Started runtime calibration

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-09 Thread Merk - Oliver
Here are the results from the output of upsc under different conditions from my Debian Test system with NUT 2.7.2 : Normal: ups.status: OL No wall power: ups.status: OB Runtime calibration (started from AP9630 web interface): ups.status: OB CAL So at this stage there is a difference! I then

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2017-01-09 Thread Merk - Oliver
Thanks for your reply. Sorry for the delay, but until yet I haven't had a subscription, so I haven't seen your answer. I can test this, I have three APC USVs, each equipped with the AP9630 network card. I need to setup a Linux test VM with NUT first. I will give the feedback as soon as I can.

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2016-12-23 Thread Charles Lepple
On Dec 20, 2016, at 9:03 AM, Merk - Oliver wrote: > > Hello, > > Last week I need to change the battery pack and then I needed to perform a > runtime calibration. I used the web interface of the AP9630 card to start the > runtime calibration. However, after 2min. of

Re: [Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2016-12-20 Thread Roger Price
On Tue, 20 Dec 2016, Merk - Oliver wrote: Last week I need to change the battery pack and then I needed to perform a runtime calibration. I used the web interface of the AP9630 card to start the runtime calibration. However, after 2min. of runtime calibration the SAN shut down! This is

[Nut-upsuser] NUT Client shuts down when performing runtime calibration on APC UPS

2016-12-20 Thread Merk - Oliver
Hello, I am using an APC UPS (Smart-UPS 2200 RM) to secure my SAN. The SAN runs on FreeBSD 9.1-RELEASE-p5 and is using NUT 2.6.5 version 2. Since the UPS has also a Network card AP9630 I am using the snmp-ups driver to connect the SAN to the UPS for signaling. Last week I need to change the