Re: [RE-wrenches] battery box fan

2008-11-07 Thread Darryl Thayer
HI Larry I am sorry I misunderstood your query, What you need is a 12 V. coil relay capable of handeling the DC fan current at 48 volts. I usually go to grainger for these, 12 volt coil (DC) and contact rating of a single pole single throw relay, or a two pole, single throw and wire the contact

Re: [RE-wrenches] battery box fan

2008-11-07 Thread Darryl Thayer
If your fan is less than 1 amp, like a small computer fan, you can power the fan directly, else you have a problem, because you have 48 volts and need a 48 volt fan or a voltage coverter 48 to 12 volts. Solar converters makes such an item aloong with others. Darryl --- On Fri, 11/7/08, Larry

Re: [RE-wrenches] battery box fan

2008-11-07 Thread jay peltz
Hi Larry, I suggest you get a 12v fan, make it easy. jay peltz power On Nov 7, 2008, at 1:29 PM, Larry Brown wrote: Wrenches. On an upgrade to an existing system, we just installed a Xantrex XW6048 inverter. We have a 48 volt dc battery box vent fan that we used to run through the relay

Re: [RE-wrenches] battery box fan

2008-11-07 Thread Allan Sindelar
Larry, Few relays are rated for 48V DC, as that DC voltage is high enough that relay life is compromised by arcing of the contacts. However, the current of the Power Vent is so tiny that this shouldn't be an issue. If you have an old open-coil power relay with a 12V coil lying around the shop, use

[RE-wrenches] battery box fan

2008-11-07 Thread Larry Brown
Wrenches. On an upgrade to an existing system, we just installed a Xantrex XW6048 inverter. We have a 48 volt dc battery box vent fan that we used to run through the relay on the old SW5548. The XW6048 has a 12 vdc aux output so I assume we need to install a relay to run the fan, 12vdc