Re: [RE-wrenches] Aurora Exeltech Inverters

2009-11-11 Thread wind...@wind-sun.com
I would add the new Exeltech grid tie inverter to that question. I see their ad in the latest HP magazine, but no info on their website about them, and no distributor seems to know much about them.

Re: [RE-wrenches] generator

2009-11-11 Thread Larry Brown
Dave, The original setup was an 1800 watt Homelite generator with two non GFI receptacles, no twist lock receptacle The client had the generator from building their house It was wired through a fused disconnect to the VFX3524 All worked fine They tried the same set up with the new Generac

Re: [RE-wrenches] generator

2009-11-11 Thread Mark Dickson
Had the exact same thing happen once after we replaced a circuit board in a FX3524. After some head scratching I went and checked over the AC connections at the inverter, which my overly helpful client had wired and found that he had switched the neutral and hot in legs. Best regards, Mark

Re: [RE-wrenches] generator

2009-11-11 Thread Mick Abraham
As a check, Larry might disconnect the Generac machine from the Outback system and everything else, then with machine not running, check for continuity from the neutral (wide) slot on the GFI receptacle and the metal frame of the generator. If there is continuity, the neutral is bonded to ground

Re: [RE-wrenches] generator

2009-11-11 Thread Kent Osterberg
Larry, Sounds like there are two neutral ground bonds: one at the generator and one at the house. This causes part of the neutral current to flow on the ground - a guaranteed way to trip the GFI. This is the catch 22 of connecting a portable generator, or one with an outlet, to a house

Re: [RE-wrenches] generator

2009-11-11 Thread Kent Osterberg
Mike, If the neutral/ground bond is removed, any outlets on the generator should also be removed so it can't be used as a portable power supply. Kent Osterberg Blue Mountain Solar Mick Abraham wrote: As a check, Larry might disconnect the Generac machine from the Outback system and

Re: [RE-wrenches] generator

2009-11-11 Thread Larry Brown
Allan, Using a T-240 fed from the 30 amp twist lock, non GFI, outlet with 240 volts and then taking the stepped down 120 volts into the Outback looks like it would solve the problem of having two neutral to ground bounds. It is a little pricey for the extra T-240 needed but it means not

Re: [RE-wrenches] generator

2009-11-11 Thread Allan Sindelar
Larry, One of my points in the HP gennie article is that you get what you pay for, and cheap generators - in this case, both the Homelite and the Generac - aren't always a good choice. The added cost of the T240 makes the great price not so great. If the customer balks, offer them the article.

[RE-wrenches] generator unbalance

2009-11-11 Thread Dana
We added a T-240 transformer to step down voltage, 240 to 120 VAC into an older system with a SW4024 this summer, and had input lead balancing issues till OB had us pull the neutral from the generator to the x-former. This cleared up some of the issue but not all of it. We even swapped out the

Re: [RE-wrenches] generator

2009-11-11 Thread Drake Chamberlin
For a test, install a three prong to two prong adaptor on the attachment plug, and see if the problem persists. The neutral to ground bond is likely made in the generator as well as in the electrical service. This will cause a current in the equipment ground, which will trip a GFCI. It

[RE-wrenches] Solar Christmas Goodies

2009-11-11 Thread Carl Adams
Hello Wrenches, Since year end projects are going to keep us crazy busy till year end, I am breaking with tradition and getting started early on my Christmas shopping. I have a tradition in my family of giving an ornament to each family member. Usually something relevant to the years experience