Re: [RE-wrenches] Couple of Qustions about AGM batteries

2010-02-01 Thread Warren Lauzon
The answer to systems not being used is nearly always leave them on float. However, 2 amps seems a bit high for AGM batteries unless you have some kind of phantom load. Equalization for AGM's is different and for a different purpose than with flooded. The current should be quite a bit less

Re: [RE-wrenches] Couple of Qustions about AGM batteries

2010-02-01 Thread Exeltech
AGM batteries in good condition and fully charged will consume approximately 1 milliamp per rated amp-hour in float mode at 25C.  Thus, your 250 amp-hour battery will require 250 milliamps at the manufacturer's rated float voltage (including temperature compensation). Discussion now turns to

[RE-wrenches] Back-up from large grid-tie system.

2010-02-01 Thread holtek
Project: 43kw system originally designed as grid-tie. 208 3ph, 6 SB7000(208). Equipment already rec'd. The curve ball.client now wants some back-up capabilities that include solar..there is a 7.92kw sub-array in the system that may be part of the solution. Any thoughts? Holt E.

Re: [RE-wrenches] Couple of Qustions about AGM batteries

2010-02-01 Thread Peter Parrish
Thanks Dan and Warren. The phantom load might be the Xantrex Prosine inverter. I'll check to see if the inverter is turned off. - Peter Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP Cert. 031806-26

[RE-wrenches] copper weatherhead?

2010-02-01 Thread Nik Ponzio
Wrenches, We have a project coming up that includes penetrating a copper roof with our PV conductors. What are your preferred methods for penetrating and flashing the conduit (going into a gable wall is not an option.) Thanks in advance. Best regards, Nik -- Nicholas Ponzio Building Energy

Re: [RE-wrenches] copper weatherhead?

2010-02-01 Thread frenergy
Nik, Is your concern the dielectric action between the copper roofing and a conventional galvanized roof jack? Bill Feather River Solar Electric 4291 Nelson St. Taylorsville, CA 95983 - Original Message - From: Nik Ponzio To: RE-wrenches Sent: Monday, February 01,

Re: [RE-wrenches] Back-up from large grid-tie system.

2010-02-01 Thread William Miller
Kelly: A big a** generator and a transfer switch. William Miller PS: Seriously, I have seen projects like this and rarely is there a natural subdivision in the power distribution that allows one to back up a portion of the loads. Backing up a huge power demand, which I assume this is, is

[RE-wrenches] Small Wind system monitoring

2010-02-01 Thread Chris Worcester
Hi fellow wind wrenches, We are searching for a reasonably priced add on wind data monitoring system that is fairly accurate to put in our quotes. What do you recommend? We used to use the NRG Wind Watcher Data Logger Kit, and the NRG Wind Explorer kits. These appear to have been replaced by the

[RE-wrenches] LAING PV direct pumps

2010-02-01 Thread Dana
Hello All, I am looking for 2 - Laing D5 solar 090 pumps [PV direct 12 vdc] with flanges ants bleeder ports. Conergy sold out and Innovative Solar who bought the Dankoff line now does not carry them. Any suggestions? Please contact off list if you supply. Thanks Dana Orzel

Re: [RE-wrenches] Small Wind system monitoring

2010-02-01 Thread Hugh
Logic energy sell a stand alone wind logger that can be used with various anemometers including the NRG maximum 40. They also do a web based logger that is very easy to set up, and stores data online. You can see an example of their web widgetry on my http://www.scoraigwind.com site. It

Re: [RE-wrenches] Small Wind system monitoring

2010-02-01 Thread Chris Worcester
Thanks to all for the quick response, and these are just the ticket! Nice going as usual, thanks guys. Sincerely, Chris Worcester Solar Wind Works NABCEP Certified PV Installer Phone: 530-582-4503 Fax: 530-582-4603 www.solarwindworks.com http://www.solarwindworks.com/

Re: [RE-wrenches] Back-up from large grid-tie system.

2010-02-01 Thread holtek
William, I would agree with generator only if there was the load demand. One thing I failed to mention is that this will be back-up for lights and communication for the campus police w/ 24hr autonomy. It looks as though the Sunny Island route is the most practical at this stage, but I am open

Re: [RE-wrenches] Small Wind system monitoring

2010-02-01 Thread roger dixon
Hi Jim. What do you have in the way of a remote data monitoring board for a 12 year old 10 kW Bergey w/a Grid Tek inverter? There are two (I think) anemometers and a wind vane on the existing 120' tower as well. It is the Liberty Science Center in Jersey City, NJ. I will be taking over the

[RE-wrenches] FRE Composites instead of rigid conduit

2010-02-01 Thread Paul Lyons
Esteemed RE-Wrenches: Have any of you had experience with using fiberglass reinforced epoxy conduit manufactured by FRE Composites (Quebec, Canada) instead of rigid conduit on the roof? I am concerned about the manufacturer's claim that the FRE conduit UV resistance is adequate for rooftop PV

Re: [RE-wrenches] Small Wind system monitoring

2010-02-01 Thread roger dixon
Sorry folks, this was intended to reply just to Jim. Pilot error...duh. Roger Dixon Certified Wind Site Assessor Distributor Installer of Solar Wind Energy Systems Skylands Renewable Energy, LLC 908.337.2057 cell 908.730.6474 fax roger.di...@skylandsre.com www.skylandsre.com Note: The

Re: [RE-wrenches] FRE Composites instead of rigid conduit

2010-02-01 Thread Dana
Paul - Is it UL listed? Is it approved for direct sunlight? Is it NEC approved? Fiberglass has not had a good reputation in direct sunlight in my experience. I am curious mostly as to its approvals. Dana Orzel Great Solar Works, Inc www.solarwork.com E -

Re: [RE-wrenches] Back-up from large grid-tie system.

2010-02-01 Thread Mick Abraham
Hello, Holt et al~ If the client only expects 24 hour autonomy, you could build/supply an uninterruptible power supply for the police loads only, with no solar recharge dedicated to that system. This would involve inverter/chargers, appropriate safety gear some monitoring, and a battery bank big

[RE-wrenches] Back-up from large grid-tie system.

2010-02-01 Thread Dana
I second Mick's appraisal here. I have clients that need 24/7 for computer but for only a few lighter loads and this has worked out well. They had frequent outages and very dirty power. They had lost a number of pieces of equipment to the surges. We used Outback with AGM batteries and a grid tie

Re: [RE-wrenches] Back-up from large grid-tie system.

2010-02-01 Thread Drake Chamberlin
Would it be possible to configure some Sunny Islands with a Sunny Boy on the 7.92 kw Sub Array?That might work with the new SB 8000US. At 10:52 AM 2/1/2010, you wrote: Project: 43kw system originally designed as grid-tie. 208 3ph, 6 SB7000(208). Equipment already rec'd. The curve

Re: [RE-wrenches] copper weatherhead?

2010-02-01 Thread William Dorsett
How about an all neoprene roof jack? Bill Dorsett SunwrightS 1715 Leavenworth Manhattan, KS 66502 Home/Office 785/539=1956 Cell 785/564-2583 wmdors...@sbcglobal.net See Amory Lovins July 08 on Charlie Rose http://www.charlierose.com/guests/amory-lovins --- On Mon, 2/1/10, frenergy