Re: [RE-wrenches] Fed. 30% grant to businesses

2010-03-04 Thread Carl Adams
Wrenches, I was just complementing the US Treasury on there swift response to the grant application. My customer submitted his application on the 13th of January. We received this response on the 26th (10 business days later). === From: treas1...@n

Re: [RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Bill Brooks
The serving transformer is also an issue. I've seen 800-amp service conductors on a 25kVA transformer. Just because you have wires large enough for a 400-amp service, does not mean you have a transformer capable of delivering 400-amps continuous. That is why you have to work with the serving utilit

Re: [RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Dave Click
Sometimes utilities will set a max too- here in Florida the investor-owned utilities have a rule that you take (d...@stc) x 0.85 to get the "AC equivalent" size of the array. That size then can't exceed 90% of the service rating. Not sure if this is an issue in other states. Scott McCalmont wr

Re: [RE-wrenches] Polycrystal PV modules with clear backer sheet: Who builds 'em?

2010-03-04 Thread Randy Brooks
Mick, Silicon Energy (www.silicon-energy.com, Arlington, WA) sells PV modules with a glass back sheet that are see through. They are heavier and pricey, but have a unique module design and mounting system. Randy Brooks Brooks Solar, Inc. Solar Power for People 140 Columbia View Chelan, WA

Re: [RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Scott McCalmont
Going all the way up to the rating of the service might not be such a good idea. The utility may use smaller wires for the service drop than you would expect based on the ampacity tables in the NEC. Considering the example of a 400 A service: - PG&E (local utility) requires 350 kcmil Aluminum cond

Re: [RE-wrenches] Polycrystal PV modules with clear backer sheet: Who builds 'em?

2010-03-04 Thread Scott McCalmont
Suntech Semi-Shade modules have a clear backing. On Thu, Mar 4, 2010 at 12:15 PM, Mick Abraham wrote: > Hi, Mechanics~ > > I like the Sanyo bifacial PV modules for several reasons but I guess the > biggest reason (for me) is the way they transmit light between the > cells...due to the clear back

Re: [RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Michael Kelly
Kirpal, That was always my interpretation as well. So in the case of a 400A service, I can backfeed 400A when utilizing a supply side connection. Others have thoughts on this? - Mike -- Michael Kelly Project Manager / Project Engineer NABCEP Certified Solar PV Installer ™ SolarFlair Energy, Inc

Re: [RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Kirpal Khalsa
Mike.i may be wrongbut I think i am rightyou are limited by the wire size feeding the supply and/or the transformer size which supplies the service.depending on the physical location of the tap you may be limited by the enclosure and the enclosure ratings as well would love to hear

[RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Michael Kelly
Hi All, Next to grounding, I find the calculation of the maximum amount of backfeed current allowed in a supply side connection to be the most vague issue in Article 690. Let's assume we have a 400A, 480/277 service in a commercial building, a 400A main service disconnect, and the jurisdiction is

[RE-wrenches] Polycrystal PV modules with clear backer sheet: Who builds 'em?

2010-03-04 Thread Mick Abraham
Hi, Mechanics~ I like the Sanyo bifacial PV modules for several reasons but I guess the biggest reason (for me) is the way they transmit light between the cells...due to the clear backer sheet. This seems dandy for carports, picnic shelters, etc. The $/watt for the Sanyo bifacials affects the pay

Re: [RE-wrenches] acre/MW

2010-03-04 Thread Nick Soleil
In the past, I have needed 6 acre/MW for poly arrays Nick Soleil Project Manager Advanced Alternative Energy Solutions, LLC PO Box 657 Petaluma, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax:707-769-9037 From: Scott McCalmont To: RE-wrenches Sen

Re: [RE-wrenches] Irradiance data

2010-03-04 Thread Nick Soleil
Aloha Folks: NREL had a book list order form years ago (which you could download online), and you could check any of the books you wanted, and they would send them to you for free! This irradiance data book was one of the free books I got at the time, plus others on BIPV and other topics.

Re: [RE-wrenches] Fwd: Re: GVFX temperatures

2010-03-04 Thread Gary Easton
Anyone know of a source for a SMA 2100? or any reasons for this inverter being hard to find? Gary Easton Appalachian Renewable Power Systems NABCEP Certified Solar PV NABCEP Certified Solar Thermal 740-277-8498 > Thankfully my MX60's software is old enough to still have an option to > control it'

[RE-wrenches] Cost per kWh

2010-03-04 Thread holtek
Can't put my hands on the equation for determining cost per kWh of a system. Brain seems to have ground faulted in remembering it correctly. Potential client with multi-oriented roof needs substantiation of additional upfront cost of micro-inverter vs. string inverter. Thought for the day: The

Re: [RE-wrenches] Generators and Grid-tie Systems

2010-03-04 Thread Tump
I have never been able to get my generators to connect w/ a grid tie inverter. The Kohler 20kW Isochronous generator electronic AVR doesn't nor does the smaller Onan, Honda or even I had a customer w/ 125kW & the SMA wouldn't latch on despite the quality of power tiring to connect w/o a load. I t