Re: [RE-wrenches] enphase & outback ac coupled

2010-04-10 Thread Andrew Truitt
Erika - I don't think you will find any major technical barriers but my understanding is that it will void the warranty on the Enphase units. We installed an AC coupled Enphase system with an SMA Sunny Island and it is humming along just fine. Andrew Truitt Standard Solar Inc. On Sat, Apr 10

[RE-wrenches] enphase & outback ac coupled

2010-04-10 Thread Erika M. Weliczko
Any issues except the usual ac coupled control mechanisms? I am looking at a way to have about 14kw of pv in a grid-tie battery backup scenario. Current plan is to use an ac-coupled system with enphase and avoid metallic conduit through the building and save on other issues. The challenges a

Re: [RE-wrenches] DC wire sizing

2010-04-10 Thread Bob-O Schultze
Of course it's not a practical solution, which is why we strived for (but rarely got) 2% VD on low voltage situations as I said in my first post. The obvious reply to this post is that your scenario isn't real world anymore. MPPT controllers fixed that. Or perhaps you advocate that MPPT controll

[RE-wrenches] DC wire sizing

2010-04-10 Thread Kent Osterberg
Here's my challenge to all of you that want to design for 1% or 1.5% voltage drop all the time: Take a 50-ft circuit carrying 40 amps at 12 volts, going to a C40 charge controller, select your wire size for 1% or 1.5% loss. You know that's not a practical solution.  I know that it makes more se

Re: [RE-wrenches] DC wire sizing

2010-04-10 Thread Kent Osterberg
Bill, The NEC is a minimum design design standard, but voltage drops are not part of the code.  The spots where voltage drop is discussed in the NEC are fine print notes that are not code and are not enforceable as code.  Furthermore those notes were written without any consideration of the ra