Re: [RE-wrenches] Heinz 57 off-grid array

2010-05-06 Thread Bob Clark
Wrenches: Thanks for all of your good feedback. I will be discussing the situation with our customer. I will let you know what the resolution is. Bob Clark SolarWind Energy Systems, LLC From: re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] NABCEP Statement about ULU

2010-05-06 Thread Bill Loesch
Hi Bob-O, Thanks for the PR update, in which one thrust appears to be an all encompasing /embracing appeal by listing the affiliations of the Board members. Any reason the website doesn't list the actual Board members _with_ their formal affiliation titles (i.e.. member, president)? I

Re: [RE-wrenches] BP Boycott?

2010-05-06 Thread Blair May
Allen, WELL SAID THANKS! -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar Sent: Wednesday, May 05, 2010 5:21 PM To: solarepiph...@gmail.com; RE-wrenches Subject: Re: [RE-wrenches] BP Boycott?

Re: [RE-wrenches] bare tinned solid copper

2010-05-06 Thread Phil Schneider
Engineer wants to see #6 above grade (fine), but #2 direct buried between ground rods (seems excessive). Phil Schneider Creative Energies On Wed, May 5, 2010 at 10:44 PM, August Goers aug...@luminalt.com wrote: Phil, The inspector wants to see #2 tinned copper for equipment ground in

Re: [RE-wrenches] bare tinned solid copper

2010-05-06 Thread Mick Abraham
Hello, all~ Since the original spec called for Cadweld joining of the various ground electrodes, all of those will be at identical ground potential. Cadwelding unifies them so thoroughly that they behave like a single electrode...but with bigger surface area. I suggest that lightning loops are

Re: [RE-wrenches] bare tinned solid copper

2010-05-06 Thread R Ray Walters
It all depends on how its done. If each electrode is attached to the next electrode by the #2 and Cadweld directly, and also connected through the required EGC, then there is a loop. Once you have the loop, the low resistance #2 cable only increases its ability to generate current from an

Re: [RE-wrenches] BP Boycott?

2010-05-06 Thread Jonathan Hill
Even Exxon tried solar back in the early 80's, but decided it wasn't profitable. Jonathan Hill, solar applications engineerSierra Solar Systems563C Idaho Maryland RoadGrass Valley, CA 95945Celebrating our 30th year in solar! On May 5, 2010, at 2:36 PM, R Ray Walters wrote:Its all too bad, because

[RE-wrenches] 10 kW Trace System

2010-05-06 Thread Peter Parrish
This one is for the grey beards. I was asked to look at a slightly funky, ca 10 year old, Grid-tie Battery Back Up System, with 2 ea SW5548s, 100 ea Astropower Ap-100s, 3 ea C-40 (I think) charge controllers, 3 ea strings of 4 ea Sun Extender PVX12100T (100 A-hr) batteries. The PV modules are

Re: [RE-wrenches] 10 kW Trace System

2010-05-06 Thread R Ray Walters
I like the SW4024, but I never liked the SW5548. It actually had less surge capability than its little brother. Either way, I would never recommend the Trace SW series for grid tie. They are very inefficient in that mode. (As for the noise, I seem to recall an issue with old SWs where the

Re: [RE-wrenches] Architects have no clue!

2010-05-06 Thread Jeff Yago
Heres another one for you to watch out for. We provided the solar design, wiring diagrams, and specified the solar system for a 112 module system going on the roof of a University Building as part of a design bid package.The installationwas awarded to alocal commercial electrical contractor. Due

[RE-wrenches] Enphase performance

2010-05-06 Thread Marco Mangelsdorf
My biz partner has an Enphase system with BP Solar mods. He believes that the web-based monitoring system may be reporting on the high side as far as kWH performance over time. That is, he suspects that what he's seeing may not be accurate. Anyone out there have a similar experience?

[RE-wrenches] Load size for off-grid lodge

2010-05-06 Thread jason pozner
Hey all, I am trying to size a PV/generator system for a 10,000 ft2 off-grid hunting/snowmobile lodge with outbuildings. The goal is to significantly reduce current generator run time. I was wondering if any of you have experience or suggestions for calculating time of use of lights, etc in a

Re: [RE-wrenches] Enphase performance

2010-05-06 Thread Randy
Hi Marco, We definitely experienced an overstatment. We have a client who installed 5kW on a string inverter and 5kW on enphase and it is that side-by-side comparison that enabled us to positively identify a problem. There was a significant overstatement of output. We finally got a Enphase

Re: [RE-wrenches] Load size for off-grid lodge

2010-05-06 Thread Allan Sindelar
Jason, We attempted this about 2-3 years ago for a project on one of Ted Turner's ranches. This was to be a top-of-the-line eco-lodge at 10,000' below a ridge in the northern Rockies in New Mexico, with two 7kW Provens and a 3-phase Sunny Boy/Sunny Island system. Due to the lack of real load