Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Marv Dargatz
This should not be troubling at all.  It is very straight forward. Because there is only one module per inverter, and the conductors are sized for all possible overcurrent conditions, no further consideration is necessary for the DC side of the circuit. For the ac side, section 690.8(A)(3) ap

Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Marv Dargatz
The CEC max power tests require continuous output power monitoring for 180 minutes.  At the end of the test, the CEC published power rating of the inverter is the manufacturer's stated max power OR the lowest power measured during the CEC test, whichever is lower.  So, most manufacturers set th

Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Mark Westbrock
The "Maximum Output Power" listed on the M190 spec sheet is 190 watts.  Upon observing output exceeding 190 watts, we questioned Enphase tech support and were told that the "actual" max output is 199 watts.  Similarly, the actual max output for the M210 is reported to be 219 watts, although the

Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Chris Worcester
Do the Enphase inverters clip the output power to their rating like other manufacturer's? So a M190 can only put out 190 watts max? I have had this question for a bit now on system performances using Enphase in designs during our cold spring and fall days. Sincerely, Chris Worcester Solar Win

[RE-wrenches] Need one Sharp 185W NT-S5E1U

2010-05-07 Thread Chris Worcester
Hi wrenches; I have a client in need of one Sharp 185W NT-S5E1U which was smashed by a rock, possibly vandalism. Please contact me off list if you have one on the back shelf! Thanks in advance. Sincerely, Chris Worcester Solar Wind Works NABCEP Certified PV Installer Phone: 530-582-4503 Fa

Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Mark Westbrock
The over-reporting of energy that Randy refers to below was much higher than any discrepancy based on monitoring resolution.  We have a pyranometer at the site, and Enphase reported energy production as high as 38% higher that predicted from irradiance data, as well as 38% higher than the strin

Re: [RE-wrenches] FW: Enphase performance

2010-05-07 Thread Kirpal Khalsa
This same issue has come up over the years for us..first with PV Powered inverters and then noticed in Fronius as well..We have noticed in most of our grid tied systems that are connected thru a "revenue grade meter" for Oregon Energy Trust production reporting, that the inverter always has

Re: [RE-wrenches] FW: Enphase performance

2010-05-07 Thread Peter Parrish
All meters are analog at the point of measurement, because the signals that are being measured are analog. What makes a meter "digital" is the conversion of the original analog data to digital format and downstream data manipulation. Therefore I doubt digital meters are fundamentally more or less a

Re: [RE-wrenches] FW: Enphase performance

2010-05-07 Thread Keith Cronin
Makes you wonder what is officially calibrated to whatis digital more accurate or analog utility meters...?? From: Marco Mangelsdorf To: RE-wrenches Cc: Douglas Bath Sent: Thu, May 6, 2010 8:11:16 PM Subject: [RE-wrenches] FW: Enphase performance Marco

Re: [RE-wrenches] Load size for off-grid lodge

2010-05-07 Thread William Miller
Friends: When faced with similar situations, we propose installation of permanent power monitoring equipment. Even if you don't get the job at this time, the client may tire of buying fuel or listening to and maintaining 24/7 generators. When re-contacted, you will have the data you need. I

Re: [RE-wrenches] FW: Enphase performance

2010-05-07 Thread Randy
Marco, My email doesn't seem to work on wrenches, so I am replying to you directly. We definitely experienced an overstatement. We have a client who installed 5kW on a string inverter and 5kW on enphase and it is that side-by-side comparison that enabled us to positively identify a proble

Re: [RE-wrenches] Load size for off-grid lodge

2010-05-07 Thread holtek
As a bit of a swerve off the path of this stringI am designing a grid-tie system for a building that is being "greenovated". Trying to lock down a LEED req'd percentage shaving of annual demand. I know there is a place to find assumptions from DOE, but I'm not that confident in those because