William, Check to make sure what Input you have selected... go to SETUP/FX/INPUT... Verify that you have the Ac Transfer control set to Gen. Make sure that you have adjusted the transfer delay cycles in the right screen... ADV/FX/GEN under Transfer delay cycles... I would set this to

Re: [RE-wrenches] Gen set problems

2010-06-15 Thread Jeff Wongstrom
William, I am having the same problem with a newly installed 8.5RES with a single VFX3648. The problem was somewhat corrected for a auto start shutdown by setting the generator cool down to one minute. This unloads the generator before the generator is shut down and eliminates the

Re: [RE-wrenches] Gen set problems

2010-06-15 Thread Jeff Wongstrom
Hello Steve, In my case, I tightened the voltage window to 110 lower, 125 upper and the transfer delay to 30. This made no difference. I did not confirm SETUP/FX/INPUT ...ac transfer control set to GEN. On Jun 15, 2010, at 7:15 AM, Steve Higgins wrote: William, Check to make sure

Re: [RE-wrenches] Gen set problems

2010-06-15 Thread Steve Higgins
Transfer delay of 30 is too long with sensitive electronics. This means that when the AC input drops to 110VAC the inverter waits 30 cycles before we disconnect from the genset. If the Ac transfer control is set to Grid instead of GEN then you would have to program these settings into the

Re: [RE-wrenches] Gen set problems

2010-06-15 Thread tump
Was gen bonding wire isolated when installed, when they come from the factory N is bonded to G. My Kohler rep won't sell me Kohlers anymore, factory will not Wtee any off grid/inverter app. Sent via BlackBerry by ATT -Original Message- From: William Miller will...@millersolar.com

Re: [RE-wrenches] Gen set problems

2010-06-15 Thread Jeff Wongstrom
I will set the transfer delay to zero next site visit. I did just confirm that the AC transfer control is set to GEN. On Jun 15, 2010, at 9:01 AM, Steve Higgins wrote: Transfer delay of 30 is too long with sensitive electronics. This means that when the AC input drops to 110VAC the

[RE-wrenches] Universal tool for PV connectors

2010-06-15 Thread Joel Davidson
10.06.2010: The Multitool - the new universal closing tool from Wieland Electric - replaces the multitude of special tools which, up to now, were necessary for the on-site assembly of photovoltaic plug connectors. Technicians can now cut and strip cables and crimp the silver plated contacts of

[RE-wrenches] Removal tool for PV connectors

2010-06-15 Thread William Miller
Colleagues: Does anyone know of a tool to remove pins from Multi-contact connectors? Thanks in advance. William Miller ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings:

Re: [RE-wrenches] Removal tool for PV connectors

2010-06-15 Thread Chris Worcester
Sounds like a dental procedure. Sincerely, Chris Worcester Solar Wind Works NABCEP Certified PV Installer Phone: 530-582-4503 Fax: 530-582-4603 http://www.solarwindworks.com/ www.solarwindworks.com mailto:ch...@solarwindworks.com ch...@solarwindworks.com Proven Energy Solutions From:

[RE-wrenches] two VFX3524's and a Franklin 3hp sub pump

2010-06-15 Thread Chris Worcester
Hello offgrid Wrenches, I just inherited an off grid system with one VFX3524 inverter running the home loads, and a 17kW Guardian Generac they use for charging (through an X-240 back into the inverter) to run their Franklin 3hp 240 VAC well pump, S. F. max amp 17.0 ( rated on its controller)

Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump

2010-06-15 Thread R Ray Walters
I've run a 3 Hp pump on a pair of Outback inverters, but it's not a done deal. As the pumps age, they start getting stickier (read more start up current needed to get them going) and wells often have silt which builds up in the pipe and pump, adding to the start up surge. I recently had a

Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump

2010-06-15 Thread Jeff Yago
We designed and installed a few off grid systems out west about 10 years ago and found all the wells there drill halfway to China. Since here in Virginia most wells hit quality water at 30 feet, we know there was no way the single SW4048 could handle a 2 or 3 HP pump. So we installed a 300 gallon

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread Jeff Yago
Well, this should start up a fire storm. I will not mention the county or state as we do work in many other areas, but today I stopped by a county building permit office to apply for a permit to install a grid-tie solar system that includes battery backup and generator, which we are adding to an

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread William Miller
Jeff: Good point made here. We too became concerned about lax enforcement some years ago. We started inviting ourselves to the Building Inspector trade group meetings. We submitted a permit application check list to the local jurisdictions. It sat on desks for a while, but eventually the

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread Nick Soleil
Hi Jeff: My standard permit docs are comprehensive, but do not include documentation regarding string sizing, thank goodness. A permit technician/ plan reviewer should not be overseeing string sizing. You should be thankful that the permit fees are so low, because that is the best thing a

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread Bill Brooks
www.solarabcs.org/permitting Check it out. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil Sent: Tuesday, June 15, 2010 5:01 PM To: RE-wrenches Subject: Re: [RE-wrenches] electrical permit requirements Hi Jeff:

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread William Miller
Nick: Rhetorical questions to follow: If you do not provide string calculations, how do you verify that Voc will not exceed NEC limits? How do you verify DC feeder ampacities? Does your jurisdiction not verify such parameters? We know you have a handle on these factors, but how about the

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread Mark Frye
Frankly, I hate to say how much I enjoyed the last inspector I was working with. Everytime he came out it was I will be retiring in 40 weeks. Just 30 weeks until I retire. And so on. It was always nice talking with him, and he never took more than one glance at the work. It didn't cost me anything

Re: [RE-wrenches] two VFX3524's and a Franklin 3hp sub pump

2010-06-15 Thread Allan Sindelar
Chris, We deal with deep wells routinely. Recently we installed a GTWB system for a very enjoyable retired couple. Their needs included the goat milker, sheep barn, two freezers and a fridge, and irrigation well pump, with the system sized for continuous operation in the event of a long-term

Re: [RE-wrenches] electrical permit requirements

2010-06-15 Thread Keith Cronin