William,
Check to make sure what Input you have selected... go to
SETUP/FX/INPUT... Verify that you have the Ac Transfer control set to
Gen.
Make sure that you have adjusted the transfer delay cycles in the right
screen... ADV/FX/GEN under Transfer delay cycles... I would set this to
William,
I am having the same problem with a newly installed 8.5RES with a
single VFX3648. The problem was somewhat corrected for a auto start
shutdown by setting the generator cool down to one minute. This
unloads the generator before the generator is shut down and
eliminates the
Hello Steve,
In my case, I tightened the voltage window to 110 lower, 125 upper
and the transfer delay to 30. This made no difference. I did not
confirm SETUP/FX/INPUT ...ac transfer control set to GEN.
On Jun 15, 2010, at 7:15 AM, Steve Higgins wrote:
William,
Check to make sure
Transfer delay of 30 is too long with sensitive electronics. This
means that when the AC input drops to 110VAC the inverter waits 30
cycles before we disconnect from the genset.
If the Ac transfer control is set to Grid instead of GEN then you would
have to program these settings into the
Was gen bonding wire isolated when installed, when they come from the factory N
is bonded to G.
My Kohler rep won't sell me Kohlers anymore, factory will not Wtee any off
grid/inverter app.
Sent via BlackBerry by ATT
-Original Message-
From: William Miller will...@millersolar.com
I will set the transfer delay to zero next site visit. I did just
confirm that the AC transfer control is set to GEN.
On Jun 15, 2010, at 9:01 AM, Steve Higgins wrote:
Transfer delay of 30 is too long with sensitive electronics. This
means that when the AC input drops to 110VAC the
10.06.2010: The Multitool - the new universal closing tool from Wieland
Electric - replaces the multitude of special tools which, up to now, were
necessary for the on-site assembly of photovoltaic plug connectors.
Technicians can now cut and strip cables and crimp the silver plated
contacts of
Colleagues:
Does anyone know of a tool to remove pins from Multi-contact connectors?
Thanks in advance.
William Miller
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options settings:
Sounds like a dental procedure.
Sincerely,
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
http://www.solarwindworks.com/ www.solarwindworks.com
mailto:ch...@solarwindworks.com ch...@solarwindworks.com
Proven Energy Solutions
From:
Hello offgrid Wrenches,
I just inherited an off grid system with one VFX3524 inverter running the
home loads, and a 17kW Guardian Generac they use for charging (through an
X-240 back into the inverter) to run their Franklin 3hp 240 VAC well pump,
S. F. max amp 17.0 ( rated on its controller)
I've run a 3 Hp pump on a pair of Outback inverters, but it's not a done deal.
As the pumps age, they start getting stickier (read more start up current
needed to get them going) and wells often have silt which builds up in the pipe
and pump, adding to the start up surge.
I recently had a
We designed and installed a few off grid systems out west about 10 years ago and found all the wells there drill halfway to China. Since here in Virginia most wells hit quality water at 30 feet, we know there was no way the single SW4048 could handle a 2 or 3 HP pump. So we installed a 300 gallon
Well, this should start up a fire storm. I will not mention the county or state as we do work in many other areas, but today I stopped by a county building permit office to apply for a permit to install a grid-tie solar system that includes battery backup and generator, which we are adding to an
Jeff:
Good point made here. We too became concerned about lax enforcement some
years ago. We started inviting ourselves to the Building Inspector trade
group meetings. We submitted a permit application check list to the local
jurisdictions. It sat on desks for a while, but eventually the
Hi Jeff:
My standard permit docs are comprehensive, but do not include documentation
regarding string sizing, thank goodness. A permit technician/ plan reviewer
should not be overseeing string sizing. You should be thankful that the permit
fees are so low, because that is the best thing a
www.solarabcs.org/permitting
Check it out.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Tuesday, June 15, 2010 5:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] electrical permit requirements
Hi Jeff:
Nick:
Rhetorical questions to follow:
If you do not provide string calculations, how do you verify that Voc will
not exceed NEC limits? How do you verify DC feeder ampacities? Does your
jurisdiction not verify such parameters? We know you have a handle on
these factors, but how about the
Frankly, I hate to say how much I enjoyed the last inspector I was working
with. Everytime he came out it was I will be retiring in 40 weeks. Just
30 weeks until I retire. And so on. It was always nice talking with him,
and he never took more than one glance at the work. It didn't cost me
anything
Chris,
We deal with deep wells routinely.
Recently we installed a GTWB system for a very enjoyable retired
couple. Their needs included the goat milker, sheep barn, two freezers
and a fridge, and irrigation well pump, with the system sized for
continuous operation in the event of a long-term
William
Good points. One thing I'd like to mention out here in the 50th state- on the
residential side, they don't do any calcs. They count on the installer. The
electrical inspectors aren't privy either or aren't very interested. Even on
some of the commercial projects, small commercial, they