HI Drake
BE CAREFULL I had a battery set explode on me due to a loose connection, it
had been charging, and I was investagating and the loose connection sparked and
BANG I was fortunatle to have my goggles on. Besure to stop charging then
vent, then investiagate.
Also I do not think the w
Drake Chamberlin wrote:
boB,
Thanks, I will check all connections when I get out there. Is there
anyway a loose connection could cook the batteries?
A loose connection, if it was like I described, would tend to
under-charge the batteries. I would think that
if there were ~that~ much of a
boB,
Thanks, I will check all connections when I get out there. Is there
anyway a loose connection could cook the batteries?
Thanks,
Drake
At 03:16 PM 8/14/2010, you wrote:
Drake Chamberlin wrote:
I called her back just now, and the voltage readings on the Mate,
MX and Trimetric all ma
You might consider using a gutter in lieu of the LB or a junction box if the
site conditions are conducive.
From: Marco Mangelsdorf
To: RE-wrenches
Sent: Sat, August 14, 2010 6:47:37 AM
Subject: [RE-wrenches] Aluminum conduit LBs
The lesson was that even if
Drake Chamberlin wrote:
I called her back just now, and the voltage readings on the Mate, MX
and Trimetric all match. Humm.
The batteries are 4, 4 1/2 year old, U.S. Battery L-16s wired in 24
volt configuration. It seems that I remember postings of Wrenches
having problems with these batte
I called her back just now, and the voltage readings on the Mate, MX
and Trimetric all match. Humm.
The batteries are 4, 4 1/2 year old, U.S. Battery L-16s wired in 24
volt configuration. It seems that I remember postings of Wrenches
having problems with these batteries. There is about 1 KW
The lesson was that even if, say, for a 2 ½ conduit says three 350 MCMs
are OK, that doesnt mean that a 2 ½ LB I was planning on using is rated
for three 350s.
For the first time ever I saw printed in the LB itself the specified max
conduct size, in this case 4/0 for a 2 ½ LB.
So for t
Any way she can get a real voltmeter? the MX60 has voltage calibration, so
does the FX it sounds like something is over charging, perhaps the generator
run? additonal details on battery bank size, array size and typical load.
Darryl
--- On Sat, 8/14/10, Drake Chamberlin
wrote:
From:
Drake,
I'd start by having her disconnect the temp sensor. If it has
failed, it can cause false voltage compensation.
However, if the MX60 is reading higher than actual, as your post
suggests, I would more expect it to regulate sooner, thus leading to
less water
Hello Wrenches,
I just got off the phone with an off grid system owner who has a
voltage discrepancy showing between the reading on her MX-60 and both
her Mate and Trimetric meter. The MX-60 shows 28.8 V and the
Trimetric and the Mate both show around 25 volts. The batteries are
using a tre