Is anyone able to run a service call in Puerto Penasco, Mexico on an Outback
Power system?
Please contact me off list. la...@starlightsolar.com
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
___
List sponsored by Home Power magazine
Hmm...no voltage...must've left the fuse out of this holder...lemme just
open it up a take a quick looksie
On Thu, Mar 29, 2012 at 3:41 PM, David Brearley <
david.brear...@solarprofessional.com> wrote:
> That was my suspicion as well. Simple wiring mistake. Inadequate
> commissioning protoco
That was my suspicion as well. Simple wiring mistake. Inadequate
commissioning protocol.
On 3/29/12 2:02 PM, "Bill Brooks" wrote:
> All,
>
> It is very likely that the something gone very wrong was a wiring mistake by
> the installing contractor. Many installers are clueless about the danger
Boy, I'm haunted with the notion that we've seen this before.. years ago. I want to say it was a simple fix. might have been something to do with NiCad batteries. Maybe low battery voltage and high start currents. I just don't remember.. maybe I wasn't here then.dbDan BrownFoxfire Energy Corp.Renew
Turning on other loads around the shop seems to work here. But we need
to have over 100 watts on (we are using lights) to prevent the
problem. It's a PITA, as it crashes the satellite internet, which
takes 20-60 minutes to boot back up.
DAN FINK
On Thu, Mar 29, 2012 at 12:12 PM, wrote:
> We've
All,
It is very likely that the something gone very wrong was a wiring mistake by
the installing contractor. Many installers are clueless about the danger and
consequences of getting the polarity wrong in strings or combiner box
circuits. It is very likely that the contractor mixed up their com
We've seen this type of problem twice with well pumps. Both times, the
problem was with a short in the load side close to the pump. One was
occasional, the other constant. Interestingly, running a large generator
seemed to "fix" the situation to the customer. In both cases, we found the
short, repa
Hi Mac;
We are having a similar problem at our metal shop with two stacked
SW4024s. They are stacked so that inverter #2 idles until something
240V is turned on -- well pump and welder are the only 240 VAC loads.
We are getting an overcurrent error and shutdown by just turning the
welder's power s
Perfect example of why it¹s a good idea to start designing and deploying
systems now that meet the fuse servicing requirements found in NEC 2011even
if these are not required by your AHJ yet.
People on this list are probably ahead of that curve. If not, you might want
to check out these articles:
Lightening? maybe a bad sensor on the SW. Mice? You might be able to Meg the Xformer. (Be careful). might be a bad contact. good luckDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Message
Subject: [RE-wrenches]
*
Rooftop solar installation sparks fires in Trenton, New Jersey*
28.03.2012: According to local news portal NJ.com, a rooftop solar
system has triggered several small fires at a recycling center in
Trenton, New Jersey. The article reports that "a major malfunction in
the rooftop solar pane
Hello wrenches,
I have a customer that I have been working with over the phone. He has a
SW 4024, with a T240 transformer feeding a 2 HP well pump on a timer. The
system has worked well for years, but recently, he has been getting
overcurrent errors when the well pump starts. It's not every ti
Most solar array string wiring is in the #10 range and NEC Table 250.122
allows a #10 to #12 bare copper ground wire connected to the back of each
module grounding lug based on staying under 100 amps max. breaker rating in
the combiner boxes. However, 250.120( C) states "equipment grounding
conduc