Re: [RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread Chris Mason
http://www.amazon.com/Extech-380260-Autoranging-Digital-Insulation/dp/B000EWW2UA/ref=sr_1_1?ie=UTF8&qid=1354065758&sr=8-1&keywords=extech+insulation $239 On Tue, Nov 27, 2012 at 7:32 PM, Robert Nuese wrote: > Thanks to the Wrenches who have offered good advice. > > In answer to several of you

Re: [RE-wrenches] Info On 2 V batteries Please

2012-11-27 Thread Jay Peltz
Hi Peter Are these 12 batteries in a large single steel case? And are they flooded or VRLA? Thx Jay Peltz power Sent from my iPhone On Nov 27, 2012, at 1:31 PM, "Parrish, Peter" wrote: > We recently purchased a battery powered forklift, with 24 ea. 2V batteries. > Approximate dimensi

Re: [RE-wrenches] Info On 2 V batteries Please

2012-11-27 Thread bob ellison
These batteries can take a 2000 or so cycles to 20% dod before they are worn out. Both numbers could be the 6 hour rate, it varies with electrolyte strength. Somewhere between 1.265 and 1.285 SG, some hi acid cells are 1.325 SG. The 24 means 24 cells, the 85 is the 85 AH plates and the 13 means 13

Re: [RE-wrenches] Info On 2 V batteries Please

2012-11-27 Thread William Miller
Peter: These batteries sound like IBE 85N batteries. See link below. I need to warn you that this company has about the worse web site in the industry. http://www.ibe-inc.com/html/altenergy.htm William At 01:31 PM 11/27/2012, you wrote: We recently purchased a battery powered forklift, w

Re: [RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread David Brearley
Someone earlier suggested contacting Solmetric in Sebastapol: http://www.solmetric.com/contact-us.html Their PVA I-V curve tracer is a great troubleshooting tool, and they also carry a Megger MIT 430 insulation tester: http://www.solmetric.com/megger-mit430.html Maybe they have a kit (PVA + Me

[RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread Robert Nuese
Thanks to the Wrenches who have offered good advice. In answer to several of you who suggested megger testing, No, I'm afraid I don't own a megger. It had become clear to me that this might well be a useful tool in my case, but the things are expensive. I've managed to install pv systems for 10 ye

Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Andrew Truitt
Bill Brooks posted this in 2008. A couple of project-specific sentences were removed to avoid confusion. "The 6kVA value comes from the California Rule 21 that I worked on. It only applies to split-phase 240V systems (6kVA on 120V). There is no specific limit for imbalance on a 3-phase service.

[RE-wrenches] Info On 2 V batteries Please

2012-11-27 Thread Parrish, Peter
We recently purchased a battery powered forklift, with 24 ea. 2V batteries. Approximate dimensions: W=5", L=6-3/16", H=~21" (hard to tell). Enersys is stamped on the top. The battery supplier claims the batteries are "24-85-13" but this refers to a 24V battery as far as I can tell. He also clai

Re: [RE-wrenches] Very small, auto-start gas generator?

2012-11-27 Thread Chris Mason
AGM are easy to ship in, in fact they are easier than flooded due to Hazmat shipping issues. What island? On Tue, Nov 27, 2012 at 7:01 PM, Dan Fink wrote: > We are looking at a load of about 100 watts, 24/7, and the locations would > be in the Caribbean with 5-6 full sun hours daily, most days.

Re: [RE-wrenches] Very small, auto-start gas generator?

2012-11-27 Thread Dan Fink
We are looking at a load of about 100 watts, 24/7, and the locations would be in the Caribbean with 5-6 full sun hours daily, most days. I don't foresee a large amount of generator run time, but storms and fog happen. This is not in the USA, so I also see issues in obtaining AGM batteries. Golf ca

Re: [RE-wrenches] Very small, auto-start gas generator?

2012-11-27 Thread Chris Mason
The problem you will face with such a small generator is the run time rating. You are likely to put a large number of hours on this and you will kill a little 2KW gas generator quickly. The service interval will be too short for this type of use. Additionally, they are generally not designed to be

Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Chris Mason
I really don't understand what your problem with this arrangement is. How would this be different from a house on phase A-B installing an inverter and the next house on Phase B-C installing an inverter? Or, installing two single phase 240V A/C units in a three phase building? Electricians have no i

Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Dave Click
I would agree that the imbalance at these power levels is not a major issue. If it appears that Phase A is most heavily-loaded, I'd install the inverters as A-B and A-C to help mitigate the existing imbalance. If you've got a lot of 1P loads on a 3P service-- lighting, office receptacles or wha

Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread Larry Crutcher, Starlight Solar Power Systems
Hi holt, Just FYI, Fronius will pay you $250 each to swap the inverters. Larry Crutcher Starlight Solar Power Systems On Nov 27, 2012, at 12:59 PM, wrote: We were asked to inspect a GT system installed by others. Service is 208 3ph with two (?) Fronius IG 4500 208v inverters. The inver

[RE-wrenches] Very small, auto-start gas generator?

2012-11-27 Thread Dan Fink
Hello esteemed Wrenches; Has anyone here ever come across a very small, quiet gasoline or propane generator (no more than 2kw) that can be auto-started? Or electronics that could do that for a stock generator? A Honda 1000i or 2000i would be ample, but is not auto start. This is for 12VDC perimete

Re: [RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread penobscotsolar
Hi Holt, We installed a commercial system a year ago for the National Park Service that was designed by a competitor (?) and signed off on by an engineer. It consisted of 13.2 kw of pv and two Fronius 7000 watt, 208 3 ph. inverters. It sounds a lot like what you are dealing with. I questioned th

Re: [RE-wrenches] Enphase voltage out of range errors

2012-11-27 Thread penobscotsolar
William, I should have mentioned that we have two strings of 11 M-215 on the system I was referring to. The error message we are getting is AC Freq. Out of Range. Sorry for any confusion. Daryl > William > > Double check your voltage drop on the AC branch circuits, and make sure > that you co

Re: [RE-wrenches] Enphase voltage out of range errors

2012-11-27 Thread William Miller
Bill: Good question. I called Enphase back and they say it is definitely a hardware problem. There are at least two registers that indicate AC line voltage and in this case they disagree, with VRMS indicating zero. Enphase has advanced diagnostics they can call up on-line, apparently. Wil

[RE-wrenches] 3 Phase With 2 Inverters?

2012-11-27 Thread holtek
We were asked to inspect a GT system installed by others. Service is 208 3ph with two (?) Fronius IG 4500 208v inverters. The inverter panel is 3ph with two 2pole breakers - one each side of the buss bar in a A/B, B/C configuration (??). Called Fronius and they said it would work, but they "don

Re: [RE-wrenches] Enphase voltage out of range errors

2012-11-27 Thread Bill Hoffer
William Double check your voltage drop on the AC branch circuits, and make sure that you consider your wiring between inverters. Remember that voltage drop is additive and each inverter will see a slightly lower voltage drop which could account for the voltage over error, especially if you are se

Re: [RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread David Brearley
Let us know what the megohmmeter says. FWIW: There is some precedent for premature product failure in a roof-integrated product manufactured by Energy Conversion Devices (Uni-Solar): http://www.utsandiego.com/news/2012/sep/14/tp-flawed-solar-panels-removed-at-schools/?print&page=all On Nov 27,

Re: [RE-wrenches] Best practices for conduit penetration on roof

2012-11-27 Thread Gary Willett
JASON: The reference temperature for the Square-D breakers is 40C/104F, as opposed to 20C/68F for the ABB breakers. The possibility of a "nuisance trip" due to derating would occur sooner for a 20A ABB breaker than for a 20A QO/QOB breaker. I received a follow-up e-mail earlier today from St

Re: [RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread Larry Crutcher, Starlight Solar Power Systems
Robert, Having installed hundreds of Uni-Solar modules, the only failure I every experienced was a framed US64 that had the PV negative short to frame. Flexing the module would create intermittent failure. You have PV laminates so your ground fault may be to the metal roof. I might be stating

Re: [RE-wrenches] Unisolar Intermittent Ground Fault

2012-11-27 Thread Steven Lawrence
Hi Robert, Get a mega Ohm meter, isolate the home runs and perform a test. You should get >550 MOhms. If not, there's something likely wrong with that string that's causing the intermittent ground fault. Or, have someone stand on the ground with a hose pointing it at the roof and try to find it

Re: [RE-wrenches] Best practices for conduit penetration on roof

2012-11-27 Thread Jason Szumlanski
We're pretty fortunate that a roof mounted readily accessible disconnect has not been a sticking point locally. I would argue that the AC disconnect is still the trunk cable connector, which can be not readily accessible. The AC breaker carrying the combined circuit output in the main distribution

Re: [RE-wrenches] PVSYST or similar analysis needed

2012-11-27 Thread Dave Click
Carl, you may also be interested in HOMER-- free 2-week trial available of the latest version (after that, $99 per 6-month renewal, despite zero updates since Nov 2010). There's also the free "legacy" version that's a few years old. http://homerenergy.com/ On 2012/11/26 22:40, Carl Adams wrot

Re: [RE-wrenches] Enphase voltage out of range errors

2012-11-27 Thread Jason Szumlanski
This has been a common error on M190's for us. Is the string center fed, or fed from one end of the 17 inverter string? Where are the failed inverters on the string in relation to the transition cable(s)? Enphase has an App Note on voltage rise that might be relevant. They recommend center feeding