Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-14 Thread Mark Frye
I am interested in the SolarBridge , it has no chasis lug so it must not require a GEC, right? So why does it not require a GEC? Is it because it is not an isolated inverter? Because it is an isolated inverter that does not have a grounded current carrying conductor on the DC side? Because it

Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-14 Thread John Berdner
August: The WEEB or other Listed grounding means between the inverter case and the structure are not "contiguous or irreversible spliced" and therefore do not meet the requirements for a GEC. If the structure is then grounded via a bolt on lug it also is not irreversible or contiguous. If you c

Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-14 Thread John Berdner
Mark: The GEC is required if the inverter bonds one of the PV conductors to ground (as Enphase does). Enphase support may not have a problem with it but not using a GEC (with all the GEC requirements) on any system with a grounded array is definitely a Code violation in NEC 2008 and 2011. I don

Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-14 Thread August Goers
Hi Mark, There have been some recent threads on this list touching on this topic. As far as I understand, Enphase microinvertes still require a GEC up to and including the 2011 NEC. I don't know about the 2014 NEC. Enphase bonds the positive DC module conductor to ground. Pages 16 and 17 of their

[RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-14 Thread Mark Frye
Does anyone have the latest on the GEC for micro-inverters/ACPV issue? I know it is still in NEC 2008 and I believe 2011 with plans to address it in 2014. I am specifically interested in the issue of GEC means continues (irreversible splices) and the whole business of the DC side of these de

Re: [RE-wrenches] Kestrel Repair

2013-01-14 Thread Roy Butler
Hi Dan, A while back, I had the dubious honor of opening one of these up. If yours has the dual stator then be prepared for a very interesting alignment procedure during reassembly.

[RE-wrenches] Kestrel Repair

2013-01-14 Thread dan