Drake,
Full sized neutrals are now required due to harmonics at least.
The cost over your quote for neutral is fixed. What is the cost for unknown
consequences if you disregard manufacturers specs?
Wallace Stahle
Future Electric Energy Co
P O Box 236
Willits, CA 95490
fut...@pacific.net
CA
Hi Wallace,
For services, at least, in the 2011 NEC, the neutral is still sized
per Table 250.66 (250.24 (C) (1).
I took Allan's suggestion and called Power One tech support back. The
neutral carries no current; it is strictly for sensing.
Drake
At 02:23 PM 6/20/2013, you wrote:
Drake,
Unfortunately, the benefits are somewhat limited since you still have to
size the neutral at the same size as your EGC, and you have to upsize
your EGC thanks to your voltage drop. So now instead of a #6 neutral,
you're running them as 8s? Hey, every bit helps...
On 2013/6/20 16:18, Drake
Hello Wrenches,
Does anyone know of a way to get Whisper 100 parts? Specifically, I need a
full brush assembly. Please contact me off list if you have any of these.
Thanks
--
Mac Lewis
*
Yo solo sé que no sé nada. -Sócrates
*
___
List
im looking for a spare set of brushes (i assume you mean slip ring assembly)
too.
todd
On Thursday, June 20, 2013 5:47pm, Mac Lewis maclew...@gmail.com said:
Hello Wrenches,
Does anyone know of a way to get Whisper 100 parts? Specifically, I need a
full brush assembly. Please
Please contact me off list. I believe I can put you in touch with a Wind
Wrench who may have some available.
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342
On Thu, Jun 20,
I am thinking of running a #4 AL neutral.
At 04:35 PM 6/20/2013, you wrote:
Unfortunately, the benefits are somewhat limited since you still
have to size the neutral at the same size as your EGC, and you have
to upsize your EGC thanks to your voltage drop. So now instead of a
#6 neutral,
Hi Max,
The 800 Amp Main Service is ITE from 1977.
It is the City of San Diego.
Best regards,
Pekka Laine
President
Photon Solar Power Inc.
www.PhotonSolarPower.com
Cell. 760-556-8170
Toll Free 888-SUN-ACDC
CA Lic. #933648
NABCEP Certified PV Installer # 032611-174
Message: 1
Date: Mon, 17
8 matches