Jerry:
The gen is powering the loads through a bypass breaker so we can't be stopping
and starting it. We did simulate an inverter start by initiating a start signal
and immediately closing the gen feed breaker. This eliminated a sync error but
did not allow the gen to charge.
WM
Miller Sol
Spell check is thew worst.
On May 4, 2014 7:41 PM, "Jerry Shafer" wrote:
> Charger set to on bit the max amps to 0 or volt setting to high. Isis you
> use the inverter to turn on the genny or did you just start it up because
> it may not connect if it did not request it that has happened to my
>
Charger set to on bit the max amps to 0 or volt setting to high. Isis you
use the inverter to turn on the genny or did you just start it up because
it may not connect if it did not request it that has happened to my
customers. Go into the gen menu and try from there.
On May 4, 2014 7:25 PM, "Willia
Jerry:
Your answer was pretty vague. What kind of mid-wire or programming error?
William
Miller Solar
> On May 4, 2014, at 7:08 PM, Jerry Shafer wrote:
>
> Sorry, Programming or mis wire is where i would put my money.
>
>> On May 3, 2014 1:07 PM, wrote:
>> Friends:
>>
>>
>>
>> We commis
Sorry, Programming or mis wire is where i would put my money.
On May 3, 2014 1:07 PM, wrote:
> Friends:
>
>
>
> We commissioned a new SI6048 3 phase system yesterday. It will create
> power but it won’t charge from the generator. This is a generator that was
> working with a 3 SI4548 system. W