the 2:1 transformer also offers ac isolation. im not so sure id want the hot
line of 120vac, via a diode, on the dc part of a system.
this configuration (known as the "DT Kludge") was a common (and expensive)
workaround for outback fx series inverters which unfortunately only had one ac
input
HI Jerry,
Just a standard bridge rectifier, with correct amp rating.
AC to diode to CC, thats it.
All regulation is via CC.
jay
On Dec 15, 2014, at 7:30 PM, Jerry Shafer wrote:
> Very interesting, what diodes did you use to rectify the AC, it sounds
> similar to the wind machine designs I h
Very interesting, what diodes did you use to rectify the AC, it sounds
similar to the wind machine designs I have worked with. Do you use a coil
to regulate the AC amps to the diodes, it seams like you would need a
"throttle control" the current someway besides the diodes them selves or
the CC.
Jer
Hi Kirk,
If you use a 200vdc midnight CC you'll have no issues.
When you rectify 120vac its up around 166vdc
( uses the peak vac which is around 170vac.)
For a 150vdc max controller ( midnite 150) or a 144vdc ( outback FM) then a
buck transformer or standard transformer is the trick to reduce t
My challenge is determining the correct 480V configuration so I can use a
3-phase Solar Edge 1 for a 12KW commercial system. The SE10K requires a
480V Wye configuration.
The main 480 panel looks straightforward. L1, L2, L3 come from below grade
to three separate busbars in the panel. A 4
Larry,
I have not found a battery charger nearly as programmable as the chargers
in inverters are, and I've sold a number of inverters over the years which
were destined to be used strictly as battery chargers.
This is actually a great use for modified-square-wave inverters. The
Magnum RD2212 has
This has been discussed on this list in years past. It is possible to use an
outback charge controller as a battery charger. You need to put the 120 AC into
a bridge rectifier, then feed the 120 DC into the controller’s PV input. So
you’ll have an 80 amp battery charger.
Kirk Herander
VT S
You can manually adjust Iotas with tweaking the potentiomiters while
monitoring it with a god volt meter. But no time adjustment.
Daniel
Daniel Tittmann
CTO
Greenwired
www.greenwired.com
dan...@greenwired.com
707-923-2001 (office)
707-206-5088 (Cell)
On Mon, Dec 15, 2014 at 4:21 PM, Windsine Inc
Check out Argus Technologies.
RoyR
On Dec 15, 2014 4:01 PM, "Larry" wrote:
> Wrenches,
>
> Does anyone know of a 120/12 volt battery charger that can be programmed
> for absorb and float voltage and time in absorb mode? I have been needing
> this product for many years but I can only find it in
Ray has it right but if he DOES try to sell back, make sure is electric meter
is the old disc type. and not de-tented. You can tell if it is de-tented by
observing it spin backwards on a sunny day. A de-tented meter will spin back
just one revolution then a pawl releases and it spins back to whe
Wrenches,
Does anyone know of a 120/12 volt battery charger that can be programmed
for absorb and float voltage and time in absorb mode? I have been
needing this product for many years but I can only find it in inverters
with built in chargers from Magnum, Outback, and Xantrex.
--
Thank you,
I have a customer who installed his own system and was happy as all get out
with it.
When they changed the laws they found that he had had been billed for his
own power for seems like around 10 years! The fellow owns a phone company,
he's no idiot. The meter got him!
Bob Ellison
From:
Todd,
Yep, I did catch that this morning.
Dave
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of toddc...@finestplanet.com
Sent: Monday, December 15, 2014 12:09 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] RE; SW4024's were off grid, now on grid AC2 Con
Hi jarmo,
We have verified this is split phase 120/240. My multimeter gets 120 L-N
and 240 L-L.
Thanks
On Dec 15, 2014 10:25 AM, wrote:
> Hi:
>
> The Generac QT02224GNAX ships as a three-phase 120/208 VAC. I believe
> the Magnum is a 120/240 VAC.
>
> JARMO
>
> _
Hi:
The Generac QT02224GNAX ships as a three-phase 120/208 VAC. I believe the
Magnum is a 120/240 VAC.
JARMO
_
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Develop
also, ac1 is grid and ac2 is gen.
todd
On Monday, December 15, 2014 8:03am, "Ray Walters" said:
What you want is already programmed into the inverter. It's called Low Battery
Transfer mode (LBX), its just a program setting on the inverter. You select
this mode in Menu 9, and the
Ah the good ol' days
A note from experience. If the meter reader/ smart meter? sees backfeed,
the utility is likely to ask questions. In my customers case, the Co-op was so
eager to prove to the Va. SCC that they were on top of net metering ( this was
the early days of net meter )--or ma
What you want is already programmed into the inverter. It's called Low
Battery Transfer mode (LBX), its just a program setting on the
inverter. You select this mode in Menu 9, and then its actual battery
voltage settings are in Menu 16.
It will not sell back in this mode, but fromHome Power Ma
The way I would do this if using outback (really what I'm familiar with) is
to set up the aux relay on the inverter to trigger an AC relay that
connected the grid to the inverters ac input using the "load shed" function.
It would trigger the relay when the batteries reached a set voltage (user
prog
Hello wrenches,
We have a newly installed system that has a 22 kW Generac Quiet Source
QT02224GNAX with a Magnum MS4448-PAE. When we start the generator, the
Magnum's internal transformer temperature climbs to overtemp (240F) within
a 2 minutes. The batteries are being floated at the time, and h
Yes it can be done
Kirk Herander
VSE
> On Dec 14, 2014, at 8:09 PM, "Dave" wrote:
>
> Here is a request for advice from one of my old off grid customers who has
> recently brought in the grid to lessen his dependence on the generator. He is
> NOT selling back to the grid.
>
> The main ques