Re: [RE-wrenches] Splices in service panel

2016-09-09 Thread August Goers
Ray, I’m intrigued by this. We’ve always gone off NEC 300.3(B): (B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway,

Re: [RE-wrenches] Splices in service panel

2016-09-09 Thread Mark Westbrock
Hi Mac, Our strictest local inspector allows us to do just what you are describing, per NEC 312.8. For the label described in 312.8(3), we make a custom label that reads: "Warning: This panel contains feed-through conductors. OCPD for these feed-through conductors are located ..." and then

Re: [RE-wrenches] Back-up generator/inverter shut-down relay

2016-09-09 Thread Mac Lewis
Hi Benn, I assume the transfer switch is not over by the generator. If that's the case, there are typically many ways to do it utilizing a contactors that senses the utility side of the transfer switch. You can also use the control signal that sends the signal to the generator to start. That

Re: [RE-wrenches] Back-up generator/inverter shut-down relay

2016-09-09 Thread Tump
Wire them to the utility side of the transfer switch, Auto restart and probably manufacture recommended method of connection when used in conjunction w/ gen set. T > On Sep 8, 2016, at 1:00 PM, Benn Kilburn wrote: > > Wrenches, > We are installing 2 SolarEdge SE7600A-US

Re: [RE-wrenches] Back-up generator/inverter shut-down relay

2016-09-09 Thread Matthew Sirum
Greetings Benn, There may be another option which would avoid extra controls/devices. The point of interconnection of the inverter output circuits could be a supply side connection; the inverter outputs could be combined and interconnected between the service point/utility meter and the utility