Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread Kienan Maxfield
Jay, I'm interested in this too, but I don't have any good answers (I was hoping that someone else would have responded by now). I know that this doesn't answer the question... but my only comment is to use a pole mount whenever possible. Rapid shutdown only applies to systems on a building or

Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread Dan Fink
A very common way around rapid shutdown for off-grid systems especially with ground or pole mounts is using a "power shed" for the BOS components.if it is not inhabited / uninhabitable then rapid shutdown is not needed per NEC 2017. Dan Fink Former Professor of Solar Energy Technology, Ecotech

[RE-wrenches] VFX slow transfer from gen

2019-02-02 Thread bruce
Fellow Head Scratchers and Gurus,I have replaced VFX Control and AC boards on an older FP2 system in order to have current firmwares compatible with new Mate3s and FM100s. I am having frequent transfer delays/ outages of 30 - 60 seconds from ags Aux off gen stop until inverter transfers and produce

Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread Darryl Thayer
Midnight solar has an RSS and Tigo has an RS4 they all need to have the rapid shut down sw turn off the inverter to stop the DC current then the module level Switches can shut off the module On Thu, Jan 31, 2019, 12:58 AM jay HI All, > > Well its the new year and Module level control is here. 690

Re: [RE-wrenches] VFX slow transfer from gen

2019-02-02 Thread Dave Angelini Offgrid Solar
Single inverter or master slave? Is there an AGS? Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 Dave bruce@willpowerelect.comDave > Fellow Head Scratchers and > Gurus,I have replaced VFX Control and A

Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread jay
HI Dan and Kienan, Yea I understand some of the work arounds, but its not always possible to work around things. At some point its going to be in a building or on the roof etc. So sounds like from the crickets that things are not quite ready yet. Better slow and ready than fast and not. t

Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread Dan Fink
Jay; Off grid we have worked through some strange requirements over the last few years, and in most it had a lot had to do with how electrical inspectors interpreted NECthey are as puzzled as we are. There were AHJs calling for giant remote-trip DC breakers on battery banks to comply with rapid

Re: [RE-wrenches] VFX slow transfer from gen

2019-02-02 Thread bruce
Found some carbon on the BBus breaker and terms. Cleaned and tightened. Seemed to make the transfers seamless in manual start/stop, and got both inverters to read much closer to the same voltage without calibrating. We'll keep fingers crossed it works as well in auto stop after battery charge. Just

Re: [RE-wrenches] module level control for offgrid

2019-02-02 Thread Lones Tuss
Hello Jay and All Concerning module level shutdown. Tigo has conducted testing and has validated the FM60/80 charge controllers with their TS4 Module Platform Imo's FireRaptor has been tested by OutBack and can be used successfully in combination with FM60/80/100 the ICS Plus and the Skybox 5