Kirk,
Could there be a loose wire connection to the breaker? That could cause it
to heat up an trip sooner than it otherwise would.
Cheers,
Dave
On Sat, May 8, 2021, 2:13 PM Kirk Herander, VSE wrote:
> I have a system where the SE1 inverter fried internally. The 60A AC
> output breaker tripp
Hi Dave,
You did get the Square D part right. See the Schneider website, which shows
that it is 600V DC and does have an off in the middle.
https://www.se.com/us/en/product/DTU361/safety-switch%2C-double-throw%2C-non-fusible%2C-30a%2C-600-vac-vdc%2C-3-poles%2C-30-hp%2C-nema-1/
Cheers,
Dave
On S
Kirk,
Have you tried IMO (https://www.imoautomation.com/). I haven't seen any
ATS units advertised, but they have a pretty extensive and reasonably
priced listing of DC control equipment.
Howie
*Howie Michaelson**Sun Catcher*
*NABCEP Certified Solar PV Installer™*
*Solar Electric Systems Sales
I think I gave you the wrong schneider P/N back tomorrow. Sorry! You
want an off in the middle and switch the 600vdc to A up or B down I think.
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060
One of the Wrenches reminded me about the Schneider Square D model
below. It is huge and not inexpensive. I thought I had found a smaller one
from Siemens but it only had a 250 vdc rating. Let us know if you find a
smaller version with 600vdc.
https://www.gordonelectricsupply.com/p/Square-D-Dtu
This whole high voltage connection discussion got me searching, and I
found Phoenix Contact makes a DIN rail mount terminal block that is 1000
v rated. That would seem to make way more sense than using MC 4
connects in a J box, and would provide the access for voltage readings
and torque check
I have a system where the SE1 inverter fried internally. The 60A AC output
breaker tripped several times, as a result of the homeowner resetting over and
over until he called me.
I replaced the inverter under warranty and all is fine, except on sunny days
the breaker will trip at about 40A,
Hello,
Any recommendations for sourcing a 600 vDC bypass / transfer switch? I know
Morningstar used to make a manual stand-alone, but now it appears to be offered
only as part of their HV charge controller. Thanks.
Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar]