I have had success with putting together either (3, for 24 v systems) or (6, 
for 48 v systems) 9 V Duracell batteries to jump start off grid OutBack systems 
when their battery banks have been unattended for too long, last one sat for a 
year & a half due to the covid before the owners got back into their remote 
cabin. The 24 v battery bank measured ~ 4 volts. I was able to re-awaken the OB 
MX60 and FX2524 long enough to have the solar kick in and start charging the 
system, keeping the inverter on long enough to get a gen set to engage 
recharging. 

What is the thought on using 9 v batteries to bring up the caps on the Magnum’s 
during initial startup?  

 

Chris Worcester

Solar Wind Works

NABCEP PV Installation Professional

Cell 530-448-9692

www.solarwindworks.com

ch...@solarwindworks.com

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Jeff 
Clearwater
Sent: Monday, June 14, 2021 9:01 AM
To: drake.chamber...@redwoodalliance.org
Cc: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Magnum MM1524AE rebuild?

 

oh and of course I put an inline fuse in the circuit.

The current that flows of course will be dependent on battery voltage and 
resistor ohms.  So with a 48 VDC pack you could go up in resistance - just 
figure per ohm - volt - amp formulas/calculator  here. 
<http://www.sengpielaudio.com/calculator-ohm.htm> 

With less than 5 amps - you'll get a nice ramp up fill of your caps on most 
inverters we use in the industry.

Hope that helps!

Jeff Clearwater
Village Power Design



Jeff Clearwater <mailto:je...@villagepowerdesign.com> 

June 14, 2021 at 8:53 AM

Hi Drake,

So it's simply a momentary bypass circuit from the Load side to the Line side 
of your Main Inverter Breaker.  So from battery side of inverter to momentary 
on-off switch to resistor to inverter side of breaker.

I used a 25 Ohm 50 watt resistor. this one 
<https://www.amazon.com/YiePhiot-Resistor-Aluminum-Wirewound-Doorbell/dp/B07MW4VHDB/ref=sr_1_13?dchild=1&keywords=YiePhiot&qid=1623685581&sr=8-13>
 

and this nice metal screw-terminal momentary on-off switch  this one 
<https://www.amazon.com/Momentary-Waterproof-Stainless-Terminal-warranty/dp/B079HR5Q4R/ref=pd_sbs_1/142-3113942-9020237?pd_rd_w=dHOiq&pf_rd_p=a5925d26-9630-40f3-a011-d858608ac88b&pf_rd_r=WSD3157P3TEAB0M4Z6PR&pd_rd_r=ab809190-b332-4f06-952b-369bf1c6a51c&pd_rd_wg=qD1Vl&pd_rd_i=B079HR5Q4R&psc=1>
 

With a Magnum MS4024 PAE on a 10 KWH LiFePO4 pack - when I push the switch 
initially about 2 amps flows - I've found I need to hold it for about 8 seconds 
for the current to drop off to about .4 amps - then when I flip the 175 AMP 
main DC inverter breaker - there is little additional current that flows into 
the inverter caps - no sparks and my BMS doesn't shut down due to overcurrent 
fault.

Hope that helps!

Best,

Jeff






_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

drake.chamber...@redwoodalliance.org 
<mailto:drake.chamber...@redwoodalliance.org> 

June 11, 2021 at 12:27 PM

 

Hello Jeff,

That sounds really useful. How do you wire this? Where do you get the momentary 
switch?

Thanks,

Drake

---

 

 

On 2021-06-09 12:13, Jeff Clearwater wrote:

Hey Dave and Wrenches,

This is why now I always install a pre-charge circuit for Magnum's and other 
inverters - especially on a Lithium pack with a BMS.  A momentary on-off switch 
and 50 watt 20 ohm resistor - $20 worth of parts = a lifetime of less stress on 
main breaker - inverter caps and battery BMS.  I recommend it for any inverter 
over 2 KW.  Many LiFePO4 BMS's will shut down when sensing that much inrush so 
it's a must on many systems.

Best,

Jeff Clearwater
Village Power Design



palumbo1...@gmail.com <mailto:palumbo1...@gmail.com> 

June 8, 2021 at 6:01 AM

 

Is a Magnum MM1524AE inverter/charger repairable and if so by whom?

It failed after being reconnected to a battery bank, the typical small spark at 
the battery terminal when being reconnected was accompanied by a popping sound 
in the Magnum. Killed the Magnum.

 

Dave Palumbo

Hyde Park, VT





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Jeff Clearwater <mailto:je...@villagepowerdesign.com> 

June 9, 2021 at 9:13 AM

Hey Dave and Wrenches,

This is why now I always install a pre-charge circuit for Magnum's and other 
inverters - especially on a Lithium pack with a BMS.  A momentary on-off switch 
and 50 watt 20 ohm resistor - $20 worth of parts = a lifetime of less stress on 
main breaker - inverter caps and battery BMS.  I recommend it for any inverter 
over 2 KW.  Many LiFePO4 BMS's will shut down when sensing that much inrush so 
it's a must on many systems.

Best,

Jeff Clearwater
Village Power Design







_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Jeff Clearwater <mailto:je...@villagelab.net> 

June 9, 2021 at 9:12 AM

Hey Dave and Wrenches,

This is why now I always install a pre-charge circuit for Magnum's and other 
inverters - especially on a Lithium pack with a BMS.  A momentary on-off switch 
and 50 watt 20 ohm resistor - $20 worth of parts = a lifetime of less stress on 
main breaker - inverter caps and battery BMS.  I recommend it for any inverter 
over 2 KW.  Many LiFePO4 BMS's will shut down when sensing that much inrush so 
it's a must on many systems.

Best,

Jeff Clearwater
Village Power Design




palumbo1...@gmail.com <mailto:palumbo1...@gmail.com> 

June 8, 2021 at 6:01 AM

Is a Magnum MM1524AE inverter/charger repairable and if so by whom? 

It failed after being reconnected to a battery bank, the typical small spark at 
the battery terminal when being reconnected was accompanied by a popping sound 
in the Magnum. Killed the Magnum.

 

Dave Palumbo

Hyde Park, VT 





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to