I agree with Dave - spring for the AC combiner. If you market is so
competitive that $75 makes a difference, move to Florida... on second
thought... :)
Jason Szumlanski
On Fri, Oct 24, 2014 at 1:39 PM, Dave Click wrote:
> Bill, typically inverters have a max OCPD that can be installed on their
It seems that 690.64(B)1 (2008) prohibits anything but landing the outputs on
dedicated breakers or disable disconnecting means.
Glenn
-Original Message-
From: "frenergy"
Sent: 10/24/2014 11:05
To: "RE-wrenches"
Subject: [RE-wrenches] AC combiners
Wrenches,
Bill, typically inverters have a max OCPD that can be installed on their
output, and these sizes are generally not large enough to accommodate
two same-model inverters. And manuals often note that you need to have a
dedicated OCPD anyway. At least if I were ever to double-up two
inverters on a
Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of frenergy
Sent: Friday, October 24, 2014 8:05 AM
To: RE-wrenches
Subject: [RE-wrenches] AC combiners
Wrenches,
...i
Wrenches,
...its the little things. Recently someone here brought up the issue
of combining AC outputs prior to backfeeding the "solar" CB in the mains panel.
In the past I've run AC outs from inverters into a small AC dist panel,
backfeeding CBs and then ran my combined AC out from a