er 01, 2008 3:51 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] DLO wires in PV systems Mike, The RHH/RHW-2 do not cross to USE-2 because they do not have any rating for UV exposure. If these conductors are run outside of conduit on the array, you need USE-2 or PV conductor.

Re: [RE-wrenches] DLO wires in PV systems

2008-12-01 Thread Michael Cook
: 'RE-wrenches' Subject: Re: [RE-wrenches] DLO wires in PV systems Mike, The RHH/RHW-2 do not cross to USE-2 because they do not have any rating for UV exposure. If these conductors are run outside of conduit on the array, you need USE-2 or PV conductor. Mark Frye Berkeley Sola

Re: [RE-wrenches] DLO wires in PV systems

2008-12-01 Thread Mark Frye
<http://www.berkeleysolar.com/> www.berkeleysolar.com _ From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Michael Cook Sent: Monday, December 01, 2008 12:47 PM To: 'RE-wrenches' Subject: [RE-wrenches] DLO wires in PV systems We have a 4KW pv system install

[RE-wrenches] DLO wires in PV systems

2008-12-01 Thread Michael Cook
We have a 4KW pv system installed and the local inspector wants to use this as a test case so he is crossing all T's and dotting all I's. Which I am happy to help him out with training his other inspectors We are running into an issue on the module output wires. USE-2 or PV rated is how the cod