Wrenches,
I noticed an error in my reply below when Allan's second comments
arrived. Correction: the battery is considered 100% discharged (not
80%) at 10.5 volts (1.75 vpc) under the conditions of use.
Kent
Kent Osterberg wrote:
William,
I'll try to add a little to Allan's and
Kent and list,
And I was half awake this morning and realized my error in yesterday's post to which you responded... I said
"A battery is considered empty at 10.75V (12V), or 1.79 VPC."
No, it's at 10.5V, or 1.75 VPC, as you have correctly stated. Sorry.
Allan
Evening all,
A quick note on DOD.
Batteries / cells are often rated at voltages above and below 1.75VPC (1.7 -
1.85 are common), so ratings should be verified with the supplier / model.
However, as anyone that has ever run a discharge test knows, the time /
available AH from 1.8 to 1.7VPC
Allan:
Is it possible to discharge a battery to 80%. What is the battery voltage
one would expect with that DOD?
William
At 02:28 PM 3/25/2011, you wrote:
William,
I use 80%, as the intent is that this is maximum, not typical. It's
directly used to calculate the battery capacity on the
William,
Here I am repeating the RE equivalent of GAAP, Generally Accepted
Accounting Principles, as applied to battery sizing...
A battery is considered empty at 10.75V (12V), or 1.79 VPC. When you
test a battery's capacity, it's generally down to this point. How
William,
I'll try to add a little to Allan's and Ronald Parades'
comments. Nearly every battery manufacturer specifies a maximum 80%
depth of discharge (DOD); that corresponds to about 10.5 volts for a
nominal 12-volt battery. Notice how close that is to the default
setting used by many
6 matches