Hi Allan;
B&B battery, which I've used for years for sealed battery applications
has excellent charts on discharge rate vs time; just what you need for
your design. I've also found them to have stable voltage under very
heavy loads (electric vehicles) right up until they're fully
discharged.
ositiveenergysolar.com; RE-wrenches
> Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing
>
> Alan,
>
> See if you can find the locked rotor amps (LRA) for this pump. Design to
> provide that much current for starting the pump. My guess is about 7-9kW for
&
You need to know the Locked Rotor Amps (LRA) and the pump class for the
pump, there are calculators on the web that can help you size an inverter
for that application.
On Wed, Feb 15, 2012 at 1:53 PM, Allan Sindelar <
al...@positiveenergysolar.com> wrote:
> **
> Esteemed fellow Wrenches,
> We nee
>[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
>Crutcher, Starlight Solar Power Systems
>Sent: Wednesday, February 15, 2012 10:38 AM
>To: al...@positiveenergysolar.com; RE-wrenches
>Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing
>
: +530.392.0356
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, February 15, 2012 9:53 AM
To: RE-wrenches
Subject: [RE-wrenches] Design Question re Battery Bank Sizing
Esteemed fellow Wrenches,
We need
oun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher,
Starlight Solar Power Systems
Sent: Wednesday, February 15, 2012 10:38 AM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing
Alan,
Alan,
See if you can find the locked rotor amps (LRA) for this pump. Design to
provide that much current for starting the pump. My guess is about 7-9kW for a
3HP.
I'm not a fan of multiple parallel strings but you are correct that parallel
strings will produce more instantaneous current. Howev
Esteemed fellow Wrenches,
We need to size a battery bank for a GTWB just for starting a well
pump. The well is on its own meter, so as long as the battery
voltage does not crash when the pump starts there will be plenty of
capacity left over for minimal loads. We'll be