Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Ray Walters
Hi Allan; B&B battery, which I've used for years for sealed battery applications has excellent charts on discharge rate vs time; just what you need for your design. I've also found them to have stable voltage under very heavy loads (electric vehicles) right up until they're fully discharged.

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread jay peltz
ositiveenergysolar.com; RE-wrenches > Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing > > Alan, > > See if you can find the locked rotor amps (LRA) for this pump. Design to > provide that much current for starting the pump. My guess is about 7-9kW for &

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Comet Systems
You need to know the Locked Rotor Amps (LRA) and the pump class for the pump, there are calculators on the web that can help you size an inverter for that application. On Wed, Feb 15, 2012 at 1:53 PM, Allan Sindelar < al...@positiveenergysolar.com> wrote: > ** > Esteemed fellow Wrenches, > We nee

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Nathan Jones
>[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry >Crutcher, Starlight Solar Power Systems >Sent: Wednesday, February 15, 2012 10:38 AM >To: al...@positiveenergysolar.com; RE-wrenches >Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing >

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Marv Dargatz
: +530.392.0356 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar Sent: Wednesday, February 15, 2012 9:53 AM To: RE-wrenches Subject: [RE-wrenches] Design Question re Battery Bank Sizing Esteemed fellow Wrenches, We need

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Brian Teitelbaum
oun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher, Starlight Solar Power Systems Sent: Wednesday, February 15, 2012 10:38 AM To: al...@positiveenergysolar.com; RE-wrenches Subject: Re: [RE-wrenches] Design Question re Battery Bank Sizing Alan,

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Larry Crutcher, Starlight Solar Power Systems
Alan, See if you can find the locked rotor amps (LRA) for this pump. Design to provide that much current for starting the pump. My guess is about 7-9kW for a 3HP. I'm not a fan of multiple parallel strings but you are correct that parallel strings will produce more instantaneous current. Howev

[RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Allan Sindelar
Esteemed fellow Wrenches, We need to size a battery bank for a GTWB just for starting a well pump. The well is on its own meter, so as long as the battery voltage does not crash when the pump starts there will be plenty of capacity left over for minimal loads.  We'll be