Re: [RE-wrenches] Flexible stranded Connectors

2014-06-16 Thread Ray Walters
FYI, I was going to get the sleeves, but they were special order and required a special crimping tool. This project was in Mexico, so I pulled the cable out and inspected it after it was torqued. I found excellent compression, and no tearing of the strands. In my opinion, the SMA connectors

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-30 Thread Glenn Burt
-wrenches.org] On Behalf Of Allan Sindelar Sent: Wednesday, April 30, 2014 11:32 AM To: RE-wrenches Cc: Positive Energy, Inc. Subject: Re: [RE-wrenches] Flexible stranded Connectors William, Ray and Wrenches, You're not alone on this issue. We faced it and did not come up with a good resol

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-30 Thread Ray Walters
I get my cable and lugs from Quick Cable but I could not find the fine strand UL listing. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 4/30/2014 8:09 AM, jay peltz wrote: Hi ray As an FYI. Most of the lugs we

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-30 Thread James Jefferson Jarvis
What I have done, and it passed muster of my AHJ, is to use a dual wire aluminum set screw lug (see picture) that is connected to the SI lug with two round copper 1/2" diameter "slugs". The cables from the battery then attach to the bolt hole on the set screw lug using a ring terminal. That all

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-30 Thread Allan Sindelar
William, Ray and Wrenches, You're not alone on this issue. We faced it and did not come up with a good resolution nearly two years ago. This is a Wrenches writeup from June 2012 that never got posted:  Four Sunny Islands and one Radian

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-30 Thread jay peltz
Hi ray As an FYI. Most of the lugs we all use are not "rated" for fine stranded wire. Quick cable is the only one I'm aware of that if you use their tool and ends says its UL for fine stranded. I prefer ferrules for those applications vs pin adapters. (Schneider XW inverter BOS box comes wit

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-29 Thread William Miller
Ray: Darn good question, especially since I will be doing the exact same thing, *tomorrow*. I have never been clear on the real problem. Fine stranded cables overheat in the wrong lugs? Is this true for mechanical or compression? Aside from code compliance, what is the best common sense appro

[RE-wrenches] Flexible stranded Connectors

2014-04-29 Thread Ray Walters
Hi All; In order to avoid any of my work showing up in someone's slideshow of horrors, I'm trying to find the correct way to wire 3 Sunny Islands with Cobra X flex cable. While it doesn't actually mention it in the SMA manual, a call to SMA tech support confirmed my suspicions: the DC lugs in