Re: [RE-wrenches] Fwd: RE: Grid neutral

2016-11-28 Thread Chris Mason
Power stations use ground return. when we constructed power stations in my electrical years, we dug extensive trenches filled with copper conductors to provide the widest earthing system. In a three phase system, only the differential current returns to the power station. That means that there is

Re: [RE-wrenches] Fwd: RE: Grid neutral

2016-11-27 Thread Allan Sindelar
Mark and all, Thank you for some very useful replies. You confirmed my understanding. You know how a customer can be so sure of (usually) himself... Mark, I don't care that much about the structure of the utility. But it's this customer's understanding of utility structure that got me the

Re: [RE-wrenches] Fwd: RE: Grid neutral

2016-11-26 Thread Drake
A 120/240 V split phase system is supplied by a center tapped 240 V transformer. The center tap is grounded, deriving the neutral. Unbalanced current from the two hot phase conductors return back through the neutral. At 08:27 PM 11/25/2016, you wrote: Wrenches, Is there such a thing as a "grid

[RE-wrenches] Fwd: RE: Grid neutral

2016-11-25 Thread Allan Sindelar
Wrenches, Is there such a thing as a "grid neutral"? I have been providing design support to a client for a large off grid system; a prepper, rare in these parts. He claims that utility current is carried in part through the ground and in part through a neutral conductor, and such a "utility