2011-04-06 Thread Kent Osterberg
Kirpal, Neither the SQFlex pump nor its accessories are UL listed. That can lead to some serious difficulties with the AHJ. Fortunately the pump can operate without any of the accessories -- neither the IO101 nor the CU200 is required. Murray, Siemens, Square D, and others make 250-Vdc 30-amp

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Mike Nelson
C though but I think it was > one of the engineers there who I discussed it with. > Nathan Jones > Power Source Solar > > > -- > *From:* Allan Sindelar > *To:* Kirpal Khalsa > *Cc:* RE-wrenches > *Sent:* Wed, April 6, 2011 6:28:35 PM > *

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread jay peltz
; Sent: Wed, April 6, 2011 6:28:35 PM > Subject: Re: [RE-wrenches] Grundfos SQ Flex > > Kirpal, > I have never tried to feed 240V to an IO101, so I don't know the answer. But > as the pump takes a maximum of only 950-1100 watts (approximate here, from > memory). The usual rea

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Allan Sindelar
Subject: Re: [RE-wrenches] Grundfos SQ Flex Kirpal, I have never tried to feed 240V to an IO101, so I don't know the answer. But as the pump takes a maximum of only 950-1100 watts (approximate here, from memory). The u

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Nathan Jones
delar To: Kirpal Khalsa Cc: RE-wrenches Sent: Wed, April 6, 2011 6:28:35 PM Subject: Re: [RE-wrenches] Grundfos SQ Flex Kirpal, I have never tried to feed 240V to an IO101, so I don't know the answer. But as the pump takes a maximum of only 950-1100 watts (approximate here, from memory).

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Allan Sindelar
Of Kirpal Khalsa Sent: Wednesday, April 06, 2011 2:55 PM To: RE-wrenches Subject: [RE-wrenches] Grundfos SQ Flex   Hi allso

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Allan Sindelar
Kirpal, I have never tried to feed 240V to an IO101, so I don't know the answer. But as the pump takes a maximum of only 950-1100 watts (approximate here, from memory). The usual reason for adding an IO101 is to allow a portable generator to back up a PV array during

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Kirpal Khalsa
Allan.According to the IO101 literature it is rated at upto 265VAC..however in all its wiring "drawings" it only shows one hot, one neutral and a ground!?? I am puzzled.? Kirpal On Wed, Apr 6, 2011 at 2:23 PM, Allan Sindelar < al...@positiveenergysolar.com> wrote: > Kirpal, > I belie

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Kirpal Khalsa
ot ever believe anything, but seriously trust through action. > > > > *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: > re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Kirpal Khalsa > *Sent:* Wednesday, April 06, 2011 2:55 PM > *To:* RE-wrenches > *Subject:*

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Dana
e-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal Khalsa Sent: Wednesday, April 06, 2011 2:55 PM To: RE-wrenches Subject: [RE-wrenches] Grundfos SQ Flex Hi allso I have a pumping project using a grundfos SQ Flex pumpIt will operate on the grid when grid is present and then swit

[RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Dana
mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Roy Butler Sent: Wednesday, April 06, 2011 3:07 PM To: RE-wrenches Subject: Re: [RE-wrenches] Grundfos SQ Flex Kirpal, Although I can't answer your IO101 question, I can tell you that the SQ Flex operates nicely for us when us

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Allan Sindelar
Kirpal, I believe that the IO101 is only designed to accept 120VAC, not 240. The supplied AC pigtail is 15A 120V, and it uses a contactor, which would be a specific voltage only. Unless I'm mistaken, you don't want to supply 220 (240) VAC. I don't have answers f

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Nathan Jones
Kirpal, I have several of these units operating with pressure tanks with no problems there. Glad to see the pressure swich being used as disconnect. We have had multiple installs where the CU200 command to stop pumping was ignored by the pump and pressure relief protection saved the day. The DC

Re: [RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Roy Butler
Kirpal, Although I can't answer your IO101 question, I can tell you that the SQ Flex operates nicely for us when used with a pressure tank/ pressure switch. As long as the pump and PV power source are sized to accommodate the additional vertical lift caused by

[RE-wrenches] Grundfos SQ Flex

2011-04-06 Thread Kirpal Khalsa
Hi allso I have a pumping project using a grundfos SQ Flex pumpIt will operate on the grid when grid is present and then switch back to solar ready if the grid power should fail.here is the set up... 5-Sanyo HIT 220's Vmp non temp adjusted is 213VDC Pump is SQFlex 16 SQF-10 will have CU

Re: [RE-wrenches] Grundfos SQ Flex Float Switch

2010-08-23 Thread Kirpal Khalsa
hultze > *Sent:* Monday, August 23, 2010 6:45 PM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Grundfos SQ Flex Float Switch > > > > Hiya Kirpal, > > They are just signal wires from the CU200. > > Cheers, Bob-O > > > > On Aug 23, 2010, at 1:54 PM, Kir

[RE-wrenches] Grundfos SQ Flex Float Switch

2010-08-23 Thread Mark Dickson
g] On Behalf Of Bob-O Schultze Sent: Monday, August 23, 2010 6:45 PM To: RE-wrenches Subject: Re: [RE-wrenches] Grundfos SQ Flex Float Switch Hiya Kirpal, They are just signal wires from the CU200. Cheers, Bob-O On Aug 23, 2010, at 1:54 PM, Kirpal Khalsa wrote: Hi All.I can't find it

Re: [RE-wrenches] Grundfos SQ Flex Float Switch

2010-08-23 Thread Bob-O Schultze
Hiya Kirpal, They are just signal wires from the CU200. Cheers, Bob-O On Aug 23, 2010, at 1:54 PM, Kirpal Khalsa wrote: Hi All.I can't find it in any of the manuals for grundfos.does anyone know if the wiring to the float switch carries current or not. The float switch has 3 #14AWG wir

Re: [RE-wrenches] Grundfos SQ Flex Float Switch

2010-08-23 Thread solardude97
y way to definitively make them shut off is to use a standard pressure switch and break the circuit between power source and the pump. From: Kirpal Khalsa To: RE-wrenches Sent: Mon, August 23, 2010 3:54:15 PM Subject: [RE-wrenches] Grundfos SQ Flex Float Switc

Re: [RE-wrenches] Grundfos SQ Flex Float Switch

2010-08-23 Thread Roy Butler
Kirpal, If you use 18/2 shielded tray cable (with all the proper insulation ratings of course) you can run that for thousands of feet. 700' is about our average run on the majority of our pump systems and it works well for us. My wire is by Omni, part

[RE-wrenches] Grundfos SQ Flex Float Switch

2010-08-23 Thread Kirpal Khalsa
Hi All.I can't find it in any of the manuals for grundfos.does anyone know if the wiring to the float switch carries current or not. The float switch has 3 #14AWG wires...I need to add about 700 feet of wire from the CU 200 controller to the storage tank.I want to use #18AWG..i

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-25 Thread Allan Sindelar
Kirpal, For the occasional odd high-current DC contactor, I like MDI. They made the mercury displacement contactors used years ago in the Ananda/APT Powercenters. Check out http://www.mdius.com/relays.php#High_Voltage to see if they have anything you can use. Allan

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-25 Thread Brian Teitelbaum
t: Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching Hi Allthanks for the good feedback on this water pumping system. Many good ideasIt looks like this is a system which can be done. I will be looking for a relay that will have the necessary voltage characteristics which will

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-25 Thread Kirpal Khalsa
> > Mark Dickson, > > NABCEP Certified Solar PV Installer ™ > > Oasis Montana Inc. > > > -- > > *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: > re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Allan Sindelar >

[RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-24 Thread Mark Dickson
: Monday, May 24, 2010 2:39 PM To: RE-wrenches Subject: Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching Mark, Your message gave me pause, as I just last week specified this setup, so I checked into it with our Grundfos rep. He said he had never heard anything recommending against the flex

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-24 Thread Allan Sindelar
Mark, Your message gave me pause, as I just last week specified this setup, so I checked into it with our Grundfos rep. He said he had never heard anything recommending against the flex in a pressure system. He said the SQF doesn't know the difference between 40 psi and 100' of head. At the end

[RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-21 Thread Mark Dickson
d Solar PV Installer T Oasis Montana Inc. _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg Sent: Thursday, May 20, 2010 5:18 PM To: RE-wrenches Subject: Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Kent Osterberg
Kirpal, None of the SQFlex equipment is UL listed.  You may find that your AHJ won't approve any of the SQFlex controls and possibly not even the pump. Kent Osterberg Blue Mountain Solar Kirpal Khalsa wrote: Hi Folks.I am working on putting together a domestic water pumping system using

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Brian Teitelbaum
...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal Khalsa Sent: Thursday, May 20, 2010 12:28 PM To: RE-wrenches Subject: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching Hi Folks.I am working on putting together a domestic water pumping system usin

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Mick Abraham
Could be as simple as installing a DC relay of appropriate coil voltage and >>> contact configuration & ratings.  Then, use the PV to power the relay and >>> the contacts to select your preferred power source.  The necessary >>> hysteresis inherent in relays would be

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread R Ray Walters
resent. Select a relay for the >> environment (enclosed is usually best), and wire it safely. This is just >> one option - but it uses off-the-shelf parts and ought to be easy to >> configure. >> >> >> Dan >> >> >> >> --- On T

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Mick Abraham
wer source. The necessary > hysteresis inherent in relays would be present. Select a relay for the > environment (enclosed is usually best), and wire it safely. This is just > one option - but it uses off-the-shelf parts and ought to be easy to > configure. > > > Dan > >

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Allan Sindelar
Kirpal, I did this about 5 years ago, on an array-direct irrigation pump with the ability for the client to run a generator when needed. Yes, it's all automatic, and no additional relay is needed. When the IO101 senses AC it automatically closes a contactor - AC coil, NO is the AC, NC is the PV

Re: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Exeltech
the environment (enclosed is usually best), and wire it safely. This is just one option - but it uses off-the-shelf parts and ought to be easy to configure. Dan --- On Thu, 5/20/10, Kirpal Khalsa wrote: From: Kirpal Khalsa Subject: [RE-wrenches] Grundfos SQ FLEX AC/DC auto switching To:

[RE-wrenches] Grundfos SQ FLEX AC/DC auto switching

2010-05-20 Thread Kirpal Khalsa
Hi Folks.I am working on putting together a domestic water pumping system using a grundfos 11 - SQF - 2. This system will be connected to a standard pressure tank and cistern and have a solar array providing primary power. However at night and on cloudy days we would like the system to switch