You should be able to go to 32kW with four Outback Radians. I agree, there
are not enough 32-100kW split phase inverter system options. With LiPO
batteries becoming popular, a high integrated charging capacity is
desirable in larger battery capacity scenarios, especially if trying to
maximize gener
The Victron Quattro (120/240) is stackable to 6 units for 30 KW of split phase
or 48 KW of 240V and 144KW of 3 phase if I’m reading the spec sheets correctly.
Sent from my iPhone
> On Feb 23, 2020, at 6:42 AM, Jay wrote:
>
> People might also look at Victron inverters.
>
> Jay
> Peltz Power
People might also look at Victron inverters.
Jay
Peltz Power.
> On Feb 23, 2020, at 3:23 AM, Jeff Clearwater
> wrote:
>
> The Sol-Ark manual indicates 240 Volt stacking to 8 units (9 units for
> 208V). They list the "12KW" off-grid output as 8 KWs each. So 64 KWs.
>
> anybody stacked a
The Sol-Ark manual indicates 240 Volt stacking to 8 units (9 units for
208V). They list the "12KW" off-grid output as 8 KWs each. So 64 KWs.
anybody stacked a signficant number of them yet?
Looking forward to hearing feedback from experienced installers.
Best,
Jeff
Allan Sindelar wrote on
...and we were told at Intersolar 2.5 years ago that the B17 was
comingstill waiting.
Bill
On 2/22/2020 6:56 PM, Allan Sindelar wrote:
Jeff, according to Midnite’s website, their B-17 inverter can be up to
40 kW in 2 kW increments.
Allan
On Feb 22, 2020, at 8:05 PM, Jeff Clearwater
Jeff, according to Midnite’s website, their B-17 inverter can be up to 40 kW in
2 kW increments.
Allan
> On Feb 22, 2020, at 8:05 PM, Jeff Clearwater
> wrote:
>
> Ahh you're right all our 120/240 volt systems are less than 24 KW. I was
> thinking of 230 V 50hz systems with multi-cluster
Jeff, according to Midnite’s website, their B-17 inverter can be up to 40 kW in
2 kW increments.
Allan
>> On Feb 22, 2020, at 8:05 PM, Jeff Clearwater
>> wrote:
> Ahh you're right all our 120/240 volt systems are less than 24 KW. I was
> thinking of 230 V 50hz systems with multi-cluster
Ahh you're right all our 120/240 volt systems are less than 24 KW. I
was thinking of 230 V 50hz systems with multi-cluster boxes.
How large can the Sol-Ark be stacked to? Anyone with large Sol-Ark
system experience?
I hear Mornignstar and MidNite are working on surge capable off-grid
inver
ts thereto.
Thank you.
From: RE-wrenches On Behalf Of wes
kennedy
Sent: Friday, February 21, 2020 2:38 PM
To: RE-wrenches ; Jeff Clearwater
Subject: Re: [RE-wrenches] High Power Split phase inverter/chargers
Hi Jeff,
I think the biggest split phase sunny island system is 4 units, so that'
alf Of wes
kennedy
Sent: Friday, February 21, 2020 2:38 PM
To: RE-wrenches ; Jeff Clearwater
Subject: Re: [RE-wrenches] High Power Split phase inverter/chargers
Hi Jeff,
I think the biggest split phase sunny island system is 4 units, so that's 24KW.
What do you do for larger s
Hi August,
Ganging multiple units gets pretty unworkable at a certain point. I actually
have a friend here in Colorado who had Tesla engineered in on a 9 power wall
system. They backed out and said they wouldn't support it, due to potential
instability.
(Also, I'm working primarily with Blue Pl
enches On Behalf Of wes
kennedy
Sent: Friday, February 21, 2020 2:38 PM
To: RE-wrenches ; Jeff Clearwater
Subject: Re: [RE-wrenches] High Power Split phase inverter/chargers
Hi Jeff,
I think the biggest split phase sunny island system is 4 units, so that's 24KW.
What do you do for
Hi Jeff,
I think the biggest split phase sunny island system is 4 units, so that's 24KW.
What do you do for larger systems? Segment the loads? Not always very
practical.
This latest opportunity is for an agricultural building that peaks at 75KW.
-Wes Kennedy 303-653-3073
On Friday, Febr
The Tesla Powerwall system has worked well for us, and be configured up in
the 50 kW + range. We've installed several 4-Powerwall systems totalling 20
kW / 54 kWh. In order to get to 50 kW battery inverter capacity, you'd need
10 Powerwalls. Now you can do multiple Gateways on site, so could
concei
Need to edit this post: The micro inverters are UL listed for grid
connected operation.
What I've noticed is that most of the AIMS inverters are not UL, ETL, or
otherwise third-party tested. And none seam to be designed for utility
interactive operation.
Kent Osterberg
Blue Mountain Solar
What I've noticed is that most of the AIMS inverters are not UL, ETL, or
otherwise third-party tested. And none seam to be designed for utility
interactive operation.
Kent Osterberg
Blue Mountain Solar
On 2/21/2020 1:37 PM, wes kennedy wrote:
Hi Jeff,
I think the biggest split phase sunny i
All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12
KW have worked flawlessly and delivered reliable power and good
monitoring for years. Less excited about my Schneider and Outback
systems due to callbacks and hassles. a bit more expensive but worth it
IMHO.
Hope that h
Hi friends,
I keep running across opportunities with 50KW-300KW peak load requirements, on
split phase services. Big homes, agriculture etc.
Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but north of
there, I am not finding many (any?) options?
Just found Aims Power 50 KW s