Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Chris Mason
Using PV and battery backup to reduce generator run time is a no-brainer, and we all are familiar with that sort of stuff. But using PV to augment a Prime Power generator is not going to work at small generator sizes for a couple of reasons. 1) Small generators are not built to run continually. 2)

Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Dave Click
The inverter to generator ratio is entirely the designer's call and comes into play for large generators (for residential systems as mentioned in earlier replies, it's a bad idea). Interconnecting in spot networks in dense urban areas has a similar issue in that the distribution system can't h

Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Chris Mason
We run into this a lot in the Caribbean. Our general rule is that it depends on the load. If it is a constant commercial load and the PV is about half of the load, no issue. But for residential and where PV exceeds the lowest load, we prefer to be on the utility side of the ATS or use a contactor o

Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Phil Forest
Interconnecting the inverter output to the utility side of the transfer switch is not necessarily an absolute rule. A knowledgeable solar EE told me a few years back, that interconnection can be made on the load side if the inverter kW output is small compared to the generator kW, that large kW

Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Daniel Young
n Sent: Tuesday, October 28, 2014 11:20 AM To: RE-wrenches Subject: Re: [RE-wrenches] Interconnection with Generator I always connect to the utility side of the transfer switch. Since the transfer switch is a listed electrical enclosure it is the best option I have used. Aaron Aaron Mandelk

Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Aaron Mandelkorn
I always connect to the utility side of the transfer switch. Since the transfer switch is a listed electrical enclosure it is the best option I have used. Aaron Aaron Mandelkorn Owner/Solar Specialist Renewable Energy Outfitters 719-221-5249 970-596-3744 www.reosolar.com reoso...@gmail.com >

Re: [RE-wrenches] Interconnection with Generator

2014-10-28 Thread Jerry Shafer
We make it a rule simple and safe. We have 3 to 500 k gen-sets and its all the same On Oct 28, 2014 4:48 AM, "Corey Shalanski" wrote: > Wrenches, > > We frequently encounter residences with backup generators. The question > that arises: how should the PV system be interconnected? > > I have searc

[RE-wrenches] Interconnection with Generator

2014-10-28 Thread Corey Shalanski
Wrenches, We frequently encounter residences with backup generators. The question that arises: how should the PV system be interconnected? I have searched the archives and found some good information about this subject, but nothing definitive. I have fallen into the habit of broadly proclaiming t