I know an electronics technician who has repaired
a couple of Trace inverters for us for a very
reasonable fee. Contact me off the list for his contact info.
At 02:27 PM 11/3/2016, you wrote:
You can replace the internal SW fans (if the fans themselves are the problem.)
BUT the replacement fa
You can replace the internal SW fans (if the fans themselves are the
problem.)
BUT the replacement fans must draw approximately the same current as the
original fans because they are powered by a current source rather than
voltage
source. i.e. If you use a fan that draws less than the fan c
Hi Mac
No don't recommend replacing internal fans
But I have installed external 120v muffin fans on the ends.
Seal up the vents around the ends so it pulls air through.
Hook the fans to the genny input.
Quick and works well
Jay
> On Nov 3, 2016, at 7:09 AM, Mac Lewis wrote:
>
> Hello Wren
Hello Wrenches,
I recently assessed a 22 year old Trace 4024. During bulk charge mode, I
noticed that the charge would go from about 18A down to 5-6A every 15-20
seconds, and then repeat the cycle. I observed this for about 5 minutes
relatively consistently I also noticed the body of the 4024 w