Re: [RE-wrenches] Leakage of current

2022-07-10 Thread Jerry Shafer via RE-wrenches
Is there any other power sources on this building, does the leak go away at night, what is the voltage of this tingle? Fun times! On Sun, Jul 10, 2022, 2:10 PM Ron Young via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I have a customer that has self installed an array on a metal

Re: [RE-wrenches] Leakage of current

2022-07-10 Thread Jay via RE-wrenches
Hi Ron I would check via clamp on meter to see if/which string of modules has current on it. Jay > On Jul 10, 2022, at 3:10 PM, Ron Young via RE-wrenches > wrote: > > I have a customer that has self installed an array on a metal roof using APS > Rapid shutdown devices. The roof rack is

[RE-wrenches] Leakage of current

2022-07-10 Thread Ron Young via RE-wrenches
I have a customer that has self installed an array on a metal roof using APS Rapid shutdown devices. The roof rack is standard rails and L-feet. It is a high voltage system that will be connected to a Sol-Ark but it has yet to be connected, just MC cables from each set of 8 panels (3