Re: [RE-wrenches] Off-grid Sunny Island to backup

2019-02-21 Thread b...@midnitesolar.com
A Sunny Island (SI) will export excess energy to the grid when the battery voltage is driven above its target voltage (IE absorb or float) so in the case of using a Classic or any other charge controller, the charge controller needs to be set to a higher voltage than the SI. Typically I re

Re: [RE-wrenches] Off-grid Sunny Island to backup

2019-02-20 Thread Mac Lewis
Hello Wrenches, I received a response from SMA about this: The newest line of Sunny Boys (SBX.XUS-40) can be used in backup systems, as long as the Country Standard is set to IslandMode60Hz and the firmware is at least 2.03.01.R. I plan on trying to look deeper into DC coupling with selling wi

Re: [RE-wrenches] Off-grid Sunny Island to backup

2019-02-18 Thread Mac Lewis
Hi Brad, I have heard that the selling from the Midnite charge controllers doesn't work real well. There is a MNSI comm box so it may be the best way (certainly the cheapest). Does anyone have experience with this scenario, good or bad? Thanks for your input as always On Mon, Feb 18, 2019 at 8

Re: [RE-wrenches] Off-grid Sunny Island to backup

2019-02-18 Thread Tump
Mac having installed quite a few of these and having the SMA SIs installed and operating in my home, ( back up & off grid/ GT) please feel free to contact me off list. I would strongly concur w/ Bradly w/ his suggesting you utilize the dc coupling. Tump > On Feb 18, 2019, at 8:19 AM, Mac Lewis

Re: [RE-wrenches] Off-grid Sunny Island to backup

2019-02-18 Thread Bradley Bassett
I think you can leave it DC coupled and enable grid tie in the Sunny Island inverters. It might not be quite as efficient but a lot more cost effective. If you don't already have it Midnite makes a comm box that makes the Classic look like an SMA device. That might be helpful to coordinate MPPT and

[RE-wrenches] Off-grid Sunny Island to backup

2019-02-18 Thread Mac Lewis
Hello Wrenches,, We have been asked to take an SMA Sunny Island System that is off-grid, and convert it to a backup system (Quad stack). Currently, this is a DC coupled system using Midnite charge controllers. We would like to add SMA grid-tied inverters to backfeed excess power. I have located