So the issue ended up being , as far as we can tell at this point , a loose
neutral connection at the first load distribution panel feeding all loads after
the inverter.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone.
Amos,
I installed an MS-4448AE (not PAE) in late 2008 that wouldn't fire up a
Buderus hydronic boiler. Ultimately it was replaced with a Lochinvar and
that solved the issue. Magnum asked for the Buderus for testing, but
that never happened, as once the problem was resolved by the heating
contr
I also have a new (7 month old) PAE system with 2-4448 Inverters (stacked) that
we are having some strange issues with. The most troublesome issue is the new
Rheem wall-hung LP instant water heater/boiler is throwing an Error Code 12
which is supposedly a “Flame Failure”. It’s a brand new inst
Long runs of URD direct buried? Just a nick into the metal can corrode
the cable all the way through over time. We use conduit for almost
everything anymore. The savings with URD doesn't pan out, when you have
to abandon the line after 10 years.
Ray Walters
Remote Solar
303 505-8760
On 1/9
I would look at connections first, lug that is not as tight as it ne we do
to be, a breaker failing, outlets that are either push in wires or have
loose connections. Eliminate what you can before looking at the inverters
On Sun, Jan 9, 2022, 11:36 AM Jeremy Rodriguez
wrote:
>
>
> Hello
> we hav
Hello
we have a lot of PAE series magnum inverters out there.
One client lately has been experiencing voltage drop and failure of PCBs in two
of his household appliances. I know it’s common to have some dimming of the
lights when a well pump or other large load kicks on, but has anyone ran ac