Wrenches,
In reference to SMA TL inverters, 600VDC residential installs,
my supplier has advised me that 600 volt double jacketed PV wire is out
and the way to go is 1000 volt PV wire. Comments? Will I be able to use
my stock of H4 connectors with the 1000V PV wire?
Thanks,
Bill
Seems to me that the best practice for TL inverters is to use
double-insulated conductors from the array string(s) to the combiner (if
used) to the inverter.
That said, there doesn't appear to be any written requirement in the NEC to
use double-jacketed conductors. So as long at the conductor
Of Marco Mangelsdorf
Sent: Thursday, October 23, 2014 9:46 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] PV wire
Seems to me that the best practice for TL inverters is to use
double-insulated conductors from the array string(s) to the combiner (if
used) to the inverter.
That said, there doesn't
Yet again this PV wire thing rears its head.
For our PV systems using transformerless (TL) inverters, our standard
practice has been to use double-insulated conductors for all DC circuits
coming into the TL inverter(s), which we believe represents the best
practice.
However, there doesn't
Marco,
For a standard 600 volt non-isolated (transformerless) inverter based
systems, you just need to make sure that your array source circuit
conductors have a photovoltaic or PV wire rating. You can also switch to
standard THWN-2 once you get into conduit.
This Solar Pro article might help:
HI Marco
I think there has been a lot of bad/old information about PV vs double
insulated wire.
However now it only listed as PV wire.
690.35 D (3)
jay
peltz power
On Oct 23, 2014, at 2:29 PM, Marco Mangelsdorf wrote:
Yet again this “PV wire” thing rears its head.
For our PV systems
on construction before buying. Not all PV Wire is the
same (or as good).
Bill.
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Kirk
Sent: Thursday, June 26, 2014 10:58 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire
Dan,
Pv wire
Of Jason Szumlanski
Sent: Thursday, June 26, 2014 11:13 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire
Yeah, 1k/2k wire shows a diameter of 0.26 on the spec sheet, or 0.053093 in^2.
Jason Szumlanski
Fafco Solar
https://wisestamp.appspot.com/pixview.gif?p=chromev=3.42.0t
Hi folks,
What is the proper approximate in2 area to use for #10 1kva/2kva pv wire for
calculating conduit fill? I'm on a job site and don't have the specs with me.
Thanks.
Kirk Herander
VSE
___
List sponsored by Redwood Alliance
List Address:
I got .0437 for RHH-2 with outer jacket in the 2011 code
Original Message
Subject: [RE-wrenches] Pv wire
From: Kirk k...@vtsolar.com
Date: Thu, June 26, 2014 1:15 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Hi folks,
What is the proper approximate in2 area to use
] On
Behalf Of d...@foxfire-energy.com
Sent: Thursday, June 26, 2014 1:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire
I got .0437 for RHH-2 with outer jacket in the 2011 code
Original Message
Subject: [RE-wrenches] Pv wire
From: Kirk k...@vtsolar.com
Date: Thu, June 26
I use this site when I need a quick answer. Use RHH (covered) with one
conductor. You get the same answer.
http://www.electrician2.com/calculators/rf_calculator.html
Jason Szumlanski
Fafco Solar
On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski ja...@fafcosolar.com
wrote:
0.0437435 per
Dan,
Pv wire is xlpe.
Kirk Herander
VSE
On Jun 26, 2014, at 1:44 PM, d...@foxfire-energy.com wrote:
I got .0437 for RHH-2 with outer jacket in the 2011 code
Original Message
Subject: [RE-wrenches] Pv wire
From: Kirk k...@vtsolar.com
Date: Thu, June 26, 2014 1:15 pm
...@foxfire-energy.com
Sent: Thursday, June 26, 2014 1:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire
I got .0437 for RHH-2 with outer jacket in the 2011 code
Original Message
Subject: [RE-wrenches] Pv wire
From: Kirk k...@vtsolar.com
Date: Thu, June 26, 2014 1:15 pm
To: RE
Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv wire
is thicker.
Kirk Herander
VSE
On Jun 26, 2014, at 1:49 PM, Jason Szumlanski ja...@fafcosolar.com wrote:
I use this site when I need a quick answer. Use RHH (covered) with one
conductor. You get the same answer.
Yeah, 1k/2k wire shows a diameter of 0.26 on the spec sheet, or 0.053093
in^2.
Jason Szumlanski
Fafco Solar
On Thu, Jun 26, 2014 at 2:06 PM, Kirk k...@vtsolar.com wrote:
Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv
wire is thicker.
Kirk Herander
VSE
On
covering electronic communications
privacy matters.
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of d...@foxfire-energy.com
Sent: Thursday, June 26, 2014 1:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire
I got .0437
Hello, Mechanix~
I've recently learned there are two flavors of 600v photovoltaic wire. I
thought all PV wire must be normally insulated plus jacketed with an
outer PVC layer but now I see some material marked as photovoltaic wire
but it only has a single layer of XLPE slightly thicker than the
From UL:
Both PV wire and USE-2 wire use thermoset insulation and jacket typically made
of XLPE or EPCV. Nevertheless, other thermoset materials such as CP over EP, CP
over EPCV, SBR/IIR/NR and EP are also available. PV wire may also be
constructed similar to Type UF but using an additional 15
Is double insulated (e.g., Falcon-brand wire) considered PV wire? That
is, the kind of conductor needed for ungrounded (DC) PV systems? Any other
non-double insulated wire type considered PV wire?
And we seem to have a consensus that once the PV wire (for an ungrounded
circuit) reaches a
I'm starting to use the SMA SB transformerless 8-10 kW inverters.
It appears that the new SMA 6-circuit combiner box is being included
whenever I order one of these buggers (at least from my distributor).
Does the double insulated PV wire have to be used all the way back to the
inverter?
690.35 (D) The photovoltaic source conductors shall consist of the
following:
(1) Nonmetallic jacketed multiconductor cables
(2) Conductors installed in raceways, or
(3) Conductors listed and identified as Photovoltaic (PV) Wire
installed as exposed, single conductors.
***
As soon