[RE-wrenches] PV wire for TLs

2016-07-17 Thread frenergy
Wrenches, In reference to SMA TL inverters, 600VDC residential installs, my supplier has advised me that 600 volt double jacketed PV wire is out and the way to go is 1000 volt PV wire. Comments? Will I be able to use my stock of H4 connectors with the 1000V PV wire? Thanks, Bill

[RE-wrenches] PV wire

2014-10-24 Thread Marco Mangelsdorf
Seems to me that the best practice for TL inverters is to use double-insulated conductors from the array string(s) to the combiner (if used) to the inverter. That said, there doesn't appear to be any written requirement in the NEC to use double-jacketed conductors. So as long at the conductor

Re: [RE-wrenches] PV wire

2014-10-24 Thread William Miller
Of Marco Mangelsdorf Sent: Thursday, October 23, 2014 9:46 PM To: 'RE-wrenches' Subject: [RE-wrenches] PV wire Seems to me that the best practice for TL inverters is to use double-insulated conductors from the array string(s) to the combiner (if used) to the inverter. That said, there doesn't

[RE-wrenches] PV wire

2014-10-23 Thread Marco Mangelsdorf
Yet again this PV wire thing rears its head. For our PV systems using transformerless (TL) inverters, our standard practice has been to use double-insulated conductors for all DC circuits coming into the TL inverter(s), which we believe represents the best practice. However, there doesn't

Re: [RE-wrenches] PV wire

2014-10-23 Thread August Goers
Marco, For a standard 600 volt non-isolated (transformerless) inverter based systems, you just need to make sure that your array source circuit conductors have a photovoltaic or PV wire rating. You can also switch to standard THWN-2 once you get into conduit. This Solar Pro article might help:

Re: [RE-wrenches] PV wire

2014-10-23 Thread jay peltz
HI Marco I think there has been a lot of bad/old information about PV vs double insulated wire. However now it only listed as PV wire. 690.35 D (3) jay peltz power On Oct 23, 2014, at 2:29 PM, Marco Mangelsdorf wrote: Yet again this “PV wire” thing rears its head. For our PV systems

Re: [RE-wrenches] Pv wire

2014-06-27 Thread Bill Brooks
on construction before buying. Not all PV Wire is the same (or as good). Bill. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk Sent: Thursday, June 26, 2014 10:58 AM To: RE-wrenches Subject: Re: [RE-wrenches] Pv wire Dan, Pv wire

Re: [RE-wrenches] Pv wire

2014-06-27 Thread Bill Brooks
Of Jason Szumlanski Sent: Thursday, June 26, 2014 11:13 AM To: RE-wrenches Subject: Re: [RE-wrenches] Pv wire Yeah, 1k/2k wire shows a diameter of 0.26 on the spec sheet, or 0.053093 in^2. Jason Szumlanski ​Fafco Solar​ https://wisestamp.appspot.com/pixview.gif?p=chromev=3.42.0t

[RE-wrenches] Pv wire

2014-06-26 Thread Kirk
Hi folks, What is the proper approximate in2 area to use for #10 1kva/2kva pv wire for calculating conduit fill? I'm on a job site and don't have the specs with me. Thanks. Kirk Herander VSE ___ List sponsored by Redwood Alliance List Address:

Re: [RE-wrenches] Pv wire

2014-06-26 Thread dan
I got .0437 for RHH-2 with outer jacket in the 2011 code Original Message Subject: [RE-wrenches] Pv wire From: Kirk k...@vtsolar.com Date: Thu, June 26, 2014 1:15 pm To: RE-wrenches re-wrenches@lists.re-wrenches.org Hi folks, What is the proper approximate in2 area to use

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Daniel Young
] On Behalf Of d...@foxfire-energy.com Sent: Thursday, June 26, 2014 1:44 PM To: RE-wrenches Subject: Re: [RE-wrenches] Pv wire I got .0437 for RHH-2 with outer jacket in the 2011 code Original Message Subject: [RE-wrenches] Pv wire From: Kirk k...@vtsolar.com Date: Thu, June 26

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Jason Szumlanski
I use this site when I need a quick answer. Use RHH (covered) with one conductor. You get the same answer. http://www.electrician2.com/calculators/rf_calculator.html Jason Szumlanski ​Fafco Solar​ On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski ja...@fafcosolar.com wrote: 0.0437435 per

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Kirk
Dan, Pv wire is xlpe. Kirk Herander VSE On Jun 26, 2014, at 1:44 PM, d...@foxfire-energy.com wrote: I got .0437 for RHH-2 with outer jacket in the 2011 code Original Message Subject: [RE-wrenches] Pv wire From: Kirk k...@vtsolar.com Date: Thu, June 26, 2014 1:15 pm

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Daniel Young
...@foxfire-energy.com Sent: Thursday, June 26, 2014 1:44 PM To: RE-wrenches Subject: Re: [RE-wrenches] Pv wire I got .0437 for RHH-2 with outer jacket in the 2011 code Original Message Subject: [RE-wrenches] Pv wire From: Kirk k...@vtsolar.com Date: Thu, June 26, 2014 1:15 pm To: RE

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Kirk
Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv wire is thicker. Kirk Herander VSE On Jun 26, 2014, at 1:49 PM, Jason Szumlanski ja...@fafcosolar.com wrote: I use this site when I need a quick answer. Use RHH (covered) with one conductor. You get the same answer.

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Jason Szumlanski
Yeah, 1k/2k wire shows a diameter of 0.26 on the spec sheet, or 0.053093 in^2. Jason Szumlanski ​Fafco Solar​ On Thu, Jun 26, 2014 at 2:06 PM, Kirk k...@vtsolar.com wrote: Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv wire is thicker. Kirk Herander VSE On

Re: [RE-wrenches] Pv wire

2014-06-26 Thread Kirk
covering electronic communications privacy matters. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of d...@foxfire-energy.com Sent: Thursday, June 26, 2014 1:44 PM To: RE-wrenches Subject: Re: [RE-wrenches] Pv wire I got .0437

[RE-wrenches] PV Wire without the outer jacket--no worries?

2014-05-15 Thread Mick Abraham
Hello, Mechanix~ I've recently learned there are two flavors of 600v photovoltaic wire. I thought all PV wire must be normally insulated plus jacketed with an outer PVC layer but now I see some material marked as photovoltaic wire but it only has a single layer of XLPE slightly thicker than the

Re: [RE-wrenches] PV Wire without the outer jacket--no worries?

2014-05-15 Thread Brian Mehalic
From UL: Both PV wire and USE-2 wire use thermoset insulation and jacket typically made of XLPE or EPCV. Nevertheless, other thermoset materials such as CP over EP, CP over EPCV, SBR/IIR/NR and EP are also available. PV wire may also be constructed similar to Type UF but using an additional 15

[RE-wrenches] PV wire

2013-06-30 Thread Marco Mangelsdorf
Is double insulated (e.g., Falcon-brand wire) considered PV wire? That is, the kind of conductor needed for ungrounded (DC) PV systems? Any other non-double insulated wire type considered PV wire? And we seem to have a consensus that once the PV wire (for an ungrounded circuit) reaches a

[RE-wrenches] PV wire/double insulated

2010-12-12 Thread Marco Mangelsdorf
I'm starting to use the SMA SB transformerless 8-10 kW inverters. It appears that the new SMA 6-circuit combiner box is being included whenever I order one of these buggers (at least from my distributor). Does the double insulated PV wire have to be used all the way back to the inverter?

Re: [RE-wrenches] PV wire/double insulated

2010-12-12 Thread Dave Click
690.35 (D) The photovoltaic source conductors shall consist of the following: (1) Nonmetallic jacketed multiconductor cables (2) Conductors installed in raceways, or (3) Conductors listed and identified as Photovoltaic (PV) Wire installed as exposed, single conductors. *** As soon