renches.org] On Behalf Of August Goers
Sent: Wednesday, October 09, 2013 3:40 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Point of connection question
William,
You have 9 M190s each running at 800 mA according to spec sheet. That equals
7.2 A nominal output current. Plus you have 10 M250s
0 A solar breaker in this
case.
Best, August
*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *William Miller
*Sent:* Wednesday, October 09, 2013 3:07 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Point of connection question
HI William;
I think you might have a problem. Looking at Enphase's ratings, the
M190 has an output rating of 800mA, while the M250 has an output rating
of 1.0 A. 10 M250s = 10 amps, 9 M190s = 7.2 amps
17.2 amps exceeds 80% of your 20 amp breaker.
I know this won't actually happen, but my und
Friends:
At the risk of asking a question that may have been asked and answered here
in the past, I wish to pose a question about Point of Connection.
Rather than outline the situation here I put it all on a web page. If any
of you have a moment to review this, I would be most appreciative