connection can be omitted and then
RS will be limited to the PV modules only.
Kevin
From: RE-wrenches On Behalf
Of Mac Lewis via RE-wrenches
Sent: January-01-24 12:00 PM
To: RE-wrenches
Cc: Mac Lewis
Subject: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
Hello Wrenches,
To: RE-wrenches
Cc: Mac Lewis
Subject: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance
Hello Wrenches,
I need to retrofit a Schneider XW+ system with a rapid shutdown system. The
owner purchased this equipment about 4-5 years ago but is trying to get it past
a very intense
Note that the MPPT disco RS works only with Schneider charge controllers.
With any other charge controllers you'll need to use Fire Raptors.
Specifically the power line type rsd do not work with classic cc. I see no
reason why the Schneider units would not meet 2020 or 2023 codes.
On Mon, Jan 1,
I had a some way similar experience I used fire raptor and added a relay to
use Raptor signal to shutdown inverter.
On Mon, Jan 1, 2024, 2:01 PM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello Wrenches,
>
> I need to retrofit a Schneider XW+ system with a rapid shutd
Hello Wrenches,
I need to retrofit a Schneider XW+ system with a rapid shutdown system.
The owner purchased this equipment about 4-5 years ago but is trying to get
it past a *very *intense inspector.
To me, it looks relatively straightforward to get NEC 2023 rapid shutdown
compliant using Tigo TS