Re: [RE-wrenches] Split Phase Load Rating

2020-05-26 Thread Allan Sindelar
I was referring only to the MS PAE series. > On May 26, 2020, at 1:51 AM, Dave Angelini Offgrid Solar > wrote: > >  > Which model magnum can do this please? > > > > Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ > e-mail

Re: [RE-wrenches] Split Phase Load Rating

2020-05-26 Thread Dave Angelini Offgrid Solar
Which model magnum can do this please? Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Mon, 25 May 2020 19:26:07 -0600, Sindelar Solar wrote: I believe that Magnum can handle an

Re: [RE-wrenches] Split Phase Load Rating

2020-05-25 Thread Sindelar Solar
I believe that Magnum can handle an imbalance of up to 85%. I haven't found this in the inverter manual, but believe that I got it from tech support. Allan On 5/25/2020 4:03 PM, Jay wrote: Hi Mark This was a big advantage of the older FX inverters was the use of the balancing transformer.

Re: [RE-wrenches] Split Phase Load Rating

2020-05-25 Thread Jay
Hi Mark The Schneider XW model is 75% of max VA per line. (6800 x .75) The radian would be something like that, but I couldn’t find it on the spec sheet. Jay > On May 25, 2020, at 3:19 PM, Mark Frye wrote: > > OK, so with a Radian or XW what is the per-phase % of total rated power?

Re: [RE-wrenches] Split Phase Load Rating

2020-05-25 Thread Jay
Hi Mark This was a big advantage of the older FX inverters was the use of the balancing transformer. The new FXR can’t use it. I can’t find but I had to call OB to get some info on how much you could out of balance a Radian inverter. It was like 60% ,could have been a bit higher but wasn’t

Re: [RE-wrenches] Split Phase Load Rating

2020-05-25 Thread Mark Frye
OK, so with a Radian or XW what is the per-phase % of total rated power? 50%? On 5/25/2020 2:16 PM, Dave Angelini Offgrid Solar wrote: From what I have seen most folks get into trouble with split phase because they are using too small of an inverter. For a home or larger I only use the big

Re: [RE-wrenches] Split Phase Load Rating

2020-05-25 Thread Dave Angelini Offgrid Solar
>From what I have seen most folks get into trouble with split phase because they are using too small of an inverter. For a home or larger I only use the big radians or an XW's. Some do have problems because they are refitting an old 120vac power system to split phase and the load panel was never

[RE-wrenches] Split Phase Load Rating

2020-05-25 Thread Mark Frye
Folks, Back again into the way back machine, I once installed a system with multiply FX's stacked in a split-phase configuration. At the advice of the engineer, I also installed an auto-transformer across the lines to help balance the per-phase loads. With the current split-phase inverters