set tha all batteries have the same thermal
conductance to ambient
Darryl
--- On Sat, 12/5/09, boB Gudgel b...@midnitesolar.com wrote:
From: boB Gudgel b...@midnitesolar.com
Subject: Re: [RE-wrenches] Strings and series of batteries with reverse
return linkup
To: RE-wrenches re-wrenches
Darryl
--- On Sat, 12/5/09, boB Gudgel b...@midnitesolar.com wrote:
From: boB Gudgel b...@midnitesolar.com
Subject: Re: [RE-wrenches] Strings and series of batteries with reverse
return linkup
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Saturday, December 5, 2009, 3:45
Ray Walters r...@solarray.com
Subject: Re: [RE-wrenches] Strings and series of batteries with reverse
return linkup
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Monday, December 7, 2009, 1:59 PM
This is an excellent
point that Jamie is making here. On electric vehicles, we do
Assume 3 parallel battery stings, with identical batteries of internal
resistance r.
Assume identical wire leads of resistance R.
Then when the batteries have the same state of charge and their internal
resistances are equal, one can solve for the current in each string.
I1 = I3
I2 = I1 r /
Antony Tersol wrote:
Assume 3 parallel battery stings, with identical batteries of internal
resistance r.
Assume identical wire leads of resistance R.
Then when the batteries have the same state of charge and their
internal resistances are equal, one can solve for the current in each
, this is significant. I
have never seen a battery set tha all batteries have the same thermal
conductance to ambient
Darryl
--- On Sat, 12/5/09, boB Gudgel b...@midnitesolar.com wrote:
From: boB Gudgel b...@midnitesolar.com
Subject: Re: [RE-wrenches] Strings and series of batteries with reverse
). dbDan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Message
Subject: Re: [RE-wrenches] Strings and series of batteries
From: Mendocino Solar Service mso...@mcn.org
Date: Thu, December 03, 2009 9:48 pm
To: RE
s.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries
Just for a contrasting opinion:
I rarely use grease or vaseline unless it proves necessary. I have
changed out battery banks after seven years and the connectors are
stil
--
From: Hugh mailto:h...@scoraigwind.co.ukh...@scoraigwind.co.uk
Sent: Thursday, December 03, 2009 8:30 AM
To: RE-wrenches
mailto:re-wrenches@lists.re-wrenches.orgre-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series
Yes, the bus bar technique will always add 1 cable and 2 connection points. And
extra cost.
As far as I can see and from what I have read in this thread, the only
advantage to the bus bar method is absolutely equal interconnection resistances
for all the strings. Maybe this advantage is only
Original Message
Subject: Re: [RE-wrenches] Strings and series of batteries
From: Allan Sindelar al...@positiveenergysolar.com
Date: Fri, December 04, 2009 9:50 am
To: "'RE-wrenches'" re-wrenches@lists.re-wrenches.org
Funny…Quick-Cote is what I referred to in my post Wedne
Sent: Friday, December 04, 2009 11:55 AM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries with reverse
return linkup
Yes, the bus bar technique will always add 1 cable and 2 connection
points. And extra cost.
As far as I can see
- Original Message -
From: Tom Elliot tell...@wagonmaker.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Friday, December 04, 2009 3:01 PM
Subject: Re: [RE-wrenches] Strings and series of batteries with
reversereturn linkup
I would love to see some studies on that Michael. I
I was just picking up on where everybody is located. The cold weather boys like
vaseline, and obviously you warm weather folks need the grease.
I think this affects the battery sizing debate too: if I size a battery for 4
days storage, it only has 2 or 3 days of storage in really cold weather.
@lists.re-wrenches.org
Sent: Wednesday, December 02, 2009 6:07 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Basically I agree about the low melting point of Vaseline, but I see it as
the canary in the coal mine: your batteries and connections shouldn't be
getting that hot
I am sure the reason for using gloves with grease is lithium based grease
stinks like 90 weight. Who wants that on their hands?
Todd
On Thursday, December 3, 2009 1:21am, R Ray Walters r...@solarray.com said:
I was just picking up on where everybody is located. The cold weather boys
like
-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl
Thayer
Sent: Wednesday, December 02, 2009 3:11 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Strings and series of batteries
I clean,apply grease, then apply antiseze to SS
Boy, this string on strings and series of strings is starting to string into a
very long list of string related emails!
We also avoid multiple strings of batteries, but sometimes this is required to
get the right combination of system voltage and amp-hour capacity. We also
agree that 3 or
Friends:
Regardless of what material you prefer to protect battery posts, I don't
recommend applying it until after the connection is torqued. The cable
ends and the terminals need to be wire brushed immediately prior to
assembly. We had to dis-assemble a set of batteries and move them for
Not to be a solar wussy, but that's my main reason for using vaseline most of
the time, when high temps aren't an issue.
I'm a solar electrician, not an auto mechanic. (also why we quit servicing
generators)
R. Walters
r...@solarray.com
Solar Engineer
On Dec 3, 2009, at 9:38 AM,
-wrenches.org] On Behalf Of James Surrette
Sent: Thursday, December 03, 2009 12:02 PM
To: RE-wrenches; jry...@netscape.com
Subject: Re: [RE-wrenches] Strings and series of batteries
Hi Jeff,
Not to plug but we (and some other vendors) have 2V L-16's on offer. So you
can get 1000AH (C/20
-0800 (PST)
Subject: Re: [RE-wrenches] Strings and series of batteries
Are they three cells in parrallel or are they one big cell?
Hi Jamie,
Have you seen any change in
cycle life by having the three cells
in the L16 connected in parallel instead of series? Just a
question that has
Just for a contrasting opinion:
I rarely use grease or vaseline unless it proves necessary. I have
changed out battery banks after seven years and the connectors are
still pristine whilst dry. I agree that sometimes there will be
localised corrosion on battery terminals. I find it rarely,
] Strings and series of batteries
Just for a contrasting opinion:
I rarely use grease or vaseline unless it proves necessary. I have
changed out battery banks after seven years and the connectors are
still pristine whilst dry. I agree that sometimes there will be
localised corrosion on battery
of batteries
It has but the one drawback is there is no bar on this bus...
From: Phil Undercufflermailto:solarp...@gmail.com
Sent: Thursday, December 03, 2009 11:46 AM
To: re-wrenches@lists.re-wrenches.orgmailto:re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series
- Original Message - From: Richard L Ratico
richard.l.rat...@valley.net
To: re-wrenches@lists.re-wrenches.org
Sent: Tuesday, December 01, 2009 5:00 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Perhaps off topic, it's been said here previously by others, but is worth
--
From: Hugh h...@scoraigwind.co.uk
Sent: Thursday, December 03, 2009 8:30 AM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries
Just for a contrasting opinion:
I rarely use grease or vaseline
...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana
Sent: Tuesday, December 01, 2009 12:58 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Strings and series of batteries
On a similar subject here -
Long ago, I had a Trojan battery rep. state that they did
-
From: Richard L Ratico richard.l.rat...@valley.net
To: re-wrenches@lists.re-wrenches.org
Sent: Tuesday, December 01, 2009 5:00 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Perhaps off topic, it's been said here previously by others, but is worth
repeating, good old Vaseline
?).
DT
--- On Wed, 12/2/09, Tom Elliot tell...@wagonmaker.com wrote:
From: Tom Elliot tell...@wagonmaker.com
Subject: Re: [RE-wrenches] Strings and series of batteries
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, December 2, 2009, 11:58 AM
Message
We cut a hole in the lid of the Vaseline can, and have a tooth brush stuck in
for applying the goo.
R. Walters
r...@solarray.com
Solar Engineer
On Dec 2, 2009, at 10:28 AM, Allan Sindelar wrote:
Years ago we began using Quick-Cote terminal corrosion protector. At about
$12 a can it has
817.917.0527
nt...@earthlink.net
www.ntrei.com
- Original Message - From: Richard L Ratico
richard.l.rat...@valley.net
To: re-wrenches@lists.re-wrenches.org
Sent: Tuesday, December 01, 2009 5:00 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Perhaps
Sent: Wednesday, December 02, 2009 8:26 AM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries
I know that CD battery does not like parallel strings and they have a
device that measures the currents in each string
I investigated a fire from
...@wagonmaker.com wrote:
From: Tom Elliot tell...@wagonmaker.com
Subject: Re: [RE-wrenches] Strings and series of batteries
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, December 2, 2009, 2:00 PM
Darryl,
Do you understand the difference between paralleling the
traditional
traditionally.
Tom
--
From: Darryl Thayer daryl_so...@yahoo.com
Sent: Wednesday, December 02, 2009 12:04 PM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries
No, Tom I am not sure that I know
: Re: [RE-wrenches] Strings and series of batteries
Darryl,
The process of paralleling through buss bars means attaching each serial
string to a pair of buss bars rather than to neighboring series pairs so
batteries aren't passing current through each other and aren't affected by
each others
/
..
- Original Message -
From: R Ray Walters r...@solarray.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, December 02, 2009 11:48 AM
Subject: Re: [RE-wrenches] Strings and series of batteries
We cut a hole in the lid of the Vaseline can, and have a tooth brush
...@wind-sun.com
Subject: Re: [RE-wrenches] Strings and series of batteries
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, December 2, 2009, 5:01 PM
Vaseline simply is not very good for
battery terminals. The melting point is too low. There are
other things that are much
I wish I understood this bus bar use better. Electrically, these seem to be the
same thing. But by using the bus bar, there has to be more cables, cable ends,
and connection points. And cost.
I just drew a battery bank (see below link to graphic), three series strings in
parallel. On the
I also have been following this thread and wondering whazzup about
buss bars being better than just parallel cables from one battery
string to the next.
Agreed that the parallel cable method is merely using the terminal of
the battery as a connector between two cables. Maybe if there's big
] On Behalf Of Dana
Sent: Tuesday, December 01, 2009 12:58 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Strings and series of batteries
On a similar subject here â
Long ago, I had a Trojan battery rep. state that they did not like to
see more than [12] L-16s in a series âparallel bank system
Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Michael
Welch
Sent: Wednesday, December 02, 2009 4:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Strings and series of batteries
I wish I understood this bus bar use better
...@starlightsolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, December 02, 2009 5:27 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Another YES for silicon. We have used it for years. A very thin coat will
last a long time. I have seen the gooey mess for heated
/
..
- Original Message - From: Larry Crutcher, Starlight Solar
la...@starlightsolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, December 02, 2009 5:27 PM
Subject: Re: [RE-wrenches] Strings and series
Problem with bussing in the Flexware, is that the bussbars only go to 1/0.
(be great if they made an attachment like Sq D, that allowed you to bring
bigger cables to their buss.)
Another reason to go to a battery buss instead of cross tying is on complicated
layouts where cross tying won't get
: Wednesday, December 02, 2009 6:24 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Strings and series of batteries
My question about the buss bar is this.
Is this something that you are fabricating or are buying and if so where and
what?
thanks,
jay
peltz power
-wrenches@lists.re-wrenches.org
Sent: Wednesday, December 02, 2009 5:27 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Another YES for silicon. We have used it for years. A very thin coat will
last a long time. I have seen the gooey mess for heated vaseline more
than once.
Larry
on the
case. Dirty car and truck batteries in damp weather often leak current.
Joel Davidson
- Original Message -
From: R Ray Walters r...@solarray.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, December 02, 2009 6:07 PM
Subject: Re: [RE-wrenches] Strings and series
Subject: Re: [RE-wrenches] Strings and series of batteries
I wish I understood this bus bar use better. Electrically, these seem to
be the same thing. But by using the bus bar, there has to be more cables,
cable ends, and connection points. And cost.
I just drew a battery bank (see below link
--
From: Michael Welch michael.we...@re-wrenches.org
Sent: Wednesday, December 02, 2009 2:00 PM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries
I wish I understood this bus bar use better
, December 02, 2009 7:07 PM
Subject: Re: [RE-wrenches] Strings and series of batteries
Basically I agree about the low melting point of Vaseline, but I see it as
the canary in the coal mine: your batteries and connections shouldn't be
getting that hot!
Anything over 85 degrees and the cycle life
...@re-wrenches.org
Sent: Wednesday, December 02, 2009 5:05 PM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Strings and series of batteries
Thanks, Tom. I think I have seen those photos before.
Am I seeing 16 cables hooked up to each bus bar? Are you using 2 cables
On a similar subject here -
Long ago, I had a Trojan battery rep. state that they did not like to see
more than [12] L-16s in a series -parallel bank system. This was due to too
many points of connection / resistance and bad communication due to
multiple flow paths.
Has anyone else heard
/
..
- Original Message -
From: Dana
To: 'RE-wrenches'
Sent: Tuesday, December 01, 2009 10:57 AM
Subject: [RE-wrenches] Strings and series of batteries
On a similar subject here -
Long ago, I had a Trojan battery rep. state that they did not like to see
more than [12] L-16s
On that note heat the Vaseline to about smoking and brush it on. It gives
you a thin coat without all the lumps and gobs of slop. I also clean and dip
the cable ends in the can, Nice smooth coating and no corrosion for years.
The hotter the better.
The occasional hating yourself while having to
Vaseline is great, but I wouldn't put it on all exposed metal surfaces',
though.
The battery parts themselves (the lead) never have a problem, so just the
copper and the bolting hardware need the treatment.
R. Walters
r...@solarray.com
Solar Engineer
On Dec 1, 2009, at 4:00 PM, Richard L
56 matches
Mail list logo