Ungrounded (transformerless) systems require PV
wire, not USE2. PV wire is listed under the ZKLA category at UL. Go
to the UL certifications page (
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/index.html )
and enter ZKLA in the "UL Category Code" box for a list of approved
The NEC requires PV wire in 690.35(D). If you are using
transformerless inverters, you should also take a look at the other
requirements of 690.35.
Regards,
Brian
To contact Brian L Crise:
Address:
16021 NE Airport Way
Portland OR, 97230
Office Phone:(503) 262-9991 x.5054
Direct line:
Hi, Mechanix~
Am I correct that the good ol' plug connector leads on many solar modules
are non-compatible with transformerless grid-tie inverters? If so...which
module mfrs have switched to the different type of wire and how can I be
sure?
Specifically, would the 2010 Sharp 230 polycrystal or
USE2
Todd
On Thursday, February 25, 2010 10:54am, Mick Abraham m...@abrahamsolar.com
said:
...and...the next time I buy #10 sunlight resistant wire for making up my own
plug extensions...should I buy a more exotic wire type and how do I know what
will work?
Thanks,
Mick Abraham,
.
--- On Thu, 2/25/10, Mick Abraham m...@abrahamsolar.com wrote:
From: Mick Abraham m...@abrahamsolar.com
Subject: [RE-wrenches] Transformerless inverters require special plug leads
on the PV modules, right?
To: RE-wrenches re-wrenches@lists.re-wrenches.org