*From:* re-wrenches-boun...@lists.re-wrenches.org [
re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Phil Schneider [
p...@creativeenergies.biz]
*Sent:* Wednesday, May 05, 2010 8:24 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] bare tinned solid copper
Wrenches,
We
Of Phil Schneider [
p...@creativeenergies.biz]
*Sent:* Wednesday, May 05, 2010 8:24 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] bare tinned solid copper
Wrenches,
We are working through submittal steps for a 75 kW ground mounted array.
The array is split into 8 subarrays
It all depends on how its done. If each electrode is attached to the next
electrode by the #2 and Cadweld directly, and also connected through the
required EGC, then there is a loop. Once you have the loop, the low resistance
#2 cable only increases its ability to generate current from an
Wrenches,
We are working through submittal steps for a 75 kW ground mounted array.
The array is split into 8 subarrays. There is a combiner or junction box
at each subarray, with a ground rod spec'd at each subarray, underneath the
box station, with a bare stranded #6 from an equipment
, Fax 323-258-8885
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Phil
Schneider
Sent: Wednesday, May 05, 2010 8:24 AM
To: RE-wrenches
Subject: [RE-wrenches] bare tinned solid copper
Wrenches,
We are working through
-wrenches
Subject: [RE-wrenches] bare tinned solid copper
Wrenches,
We are working through submittal steps for a 75 kW ground mounted array. The
array is split into 8 subarrays. There is a combiner or junction box at each
subarray, with a ground rod spec'd at each subarray, underneath the box