2010-01-01 Thread Darryl Thayer
power. Presently the max number of 3 phase you can stack is one using the master slave, however this has changed I think. Darryl --- On Thu, 12/31/09, Nik Ponzio npon...@buildingenergyus.com wrote: From: Nik Ponzio npon...@buildingenergyus.com Subject: [RE-wrenches] dual stacked inverters

Re: [RE-wrenches] dual stacked inverters on 208V service

2010-01-01 Thread William Miller
Colleagues: We have an 8 stack Outback system on a three phase off-grid application. This works because the entire plant is using only two phases of an open-delta wired generator system, the phases being on the opposite end of the center tapped generator windings. We provide 120/240 feeds.

Re: [RE-wrenches] dual stacked inverters on 208V service

2009-12-31 Thread Mark Frye
-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye Sent: Thursday, December 31, 2009 1:53 PM To: npon...@buildingenergyus.com; 'RE-wrenches' Subject: Re: [RE-wrenches] dual stacked inverters on 208V service Not syncing or not seeing AC line

Re: [RE-wrenches] dual stacked inverters on 208V service

2009-12-31 Thread Kent Osterberg
Nik, 120/208 has a 120 degree phase angle between legs, same as three-phase but you only have two legs. Check with Outback tech support, but I believe the GTFX inverter can only be stacked in systems with 120/240 split phase (180 degrees between legs). If there are no 208 loads, just unplug

Re: [RE-wrenches] dual stacked inverters on 208V service

2009-12-31 Thread Kirk Herander, VSE
...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nik Ponzio Sent: Thursday, December 31, 2009 4:15 PM To: RE-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] dual stacked inverters on 208V service Hi Gang, I have a problem. We are installing

Re: [RE-wrenches] dual stacked inverters on 208V service

2009-12-31 Thread dan
Ho and all that. dbDan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Message Subject: Re: [RE-wrenches] dual stacked inverters on 208V service From: "Mark Frye" ma...@berkeleysolar.com Date: Thu

Re: [RE-wrenches] dual stacked inverters on 208V service

2009-12-31 Thread David Katz
Nik, Since you cannot operate 2 inverters in a 3 phase mode, they will need to operate independently, so don't try to sync them. Operate both independently. if the building is set up for 120/208 there is not 240 anyway. You could stack them in 120V synchronized and connected across a