Subject: Re: [RE-wrenches] generator search
From: Jerry Shafer <jerrysgarag...@gmail.com>
Date: Tue, April 10, 2018 12:55 pm
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Jay we have used the Cummins machines and have bee
Jay we have used the Cummins machines and have been very happy,you will
need a battery charger to maintain the SOC as the cpu has a 350 to 500 ma
draw.
Jerry
On Mon, Apr 9, 2018, 10:15 AM David Katz wrote:
> Check to see if it has a 120 vac requirement to float the
Ray <r...@solarray.com>
*Sent:* Monday, April 9, 2018 7:14 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] generator search
We've had gen sets at 11,000 ft and way below zero start on propane
for decades without using the block or water heaters. Ridiculous
electric h
ay
<r...@solarray.com>
Sent: Monday, April 9, 2018 7:14 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] generator search
We've had gen sets at 11,000 ft and way below zero start on propane for
decades without using the block or water heaters. Ridiculous electric he
We've had gen sets at 11,000 ft and way below zero start on propane
for decades without using the block or water heaters. Ridiculous
electric heating loads on the other hand are a very bad idea off grid.
Just make sure the propane supply lines are large enough so the pressure
regulator
Hi all.
This unit will be in a warm climate so no problems there.
Are you all saying the build in AC/shore power charger is extremely
inefficient?
Jay
> On Apr 9, 2018, at 1:46 PM, Michael Morningstar
> wrote:
>
> Yes, the Cummins technician that commissions
Yes, the Cummins technician that commissions our generators insists that
locations with consistent low’s below 15F require the coolant heater. All but
two of my installs(outdoor) have omitted connecting the heater, and have seen
some brief sub-0 temperatures but generally average mid-30s. One
, then you shouldn't need to use a
120V charger at all
Thanks,
Kienan
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of
David Katz <dk...@backwoodssolar.com>
Sent: Monday, April 9, 2018 2:14 PM
To: RE-wrenches
Subject: Re:
They do have a battery charger that requires a 120V circuit, and it does draw
more than one would like. I run a circuit over and install a tiny battery
tender rather than use the factory charger. With a good starter battery and a
weekly exercise cycle of thirty minutes, I have found that my
Check to see if it has a 120 vac requirement to float the battery. The 20
kw one I have has a big electrical drain
David
On Mon, Apr 9, 2018 at 11:50 AM jay wrote:
> HI All,
>
> I’ve got a new project wanting a 22-25kw single phase 120/240vac water
> cooled propane sound
Jay, I’ve had really good luck with the Cummins RS22. In fact it’s the only
propane generator I will use unless it’s for a small system, then I specify
Honda ’s with a propane conversion from GenConnect. Half a dozen RS22’s with
enclosures and maybe a dozen without, placed in buildings. No
HI All,
I’ve got a new project wanting a 22-25kw single phase 120/240vac water cooled
propane sound attenuated generator for an off grid situation. I’m not going to
be
With AGS activation.
I”ve been looking at the Kohler 24 RCL ( meets all the above criteria) but I’m
checking to see if I