il.com>
(801) 631-5584 (Cell)
From: RE-wrenches on behalf of Dave
Tedeyan
Sent: Friday, May 3, 2019 3:05 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] large(ish) AC coupled battery backup
Kienan,
Thanks for the info here. That is really interesting about the 6kw limitation.
Ou
V simultaneously.
>
> Hope this is somewhat helpful.
>
> Thanks,
> Kienan
>
>
> *Maxfield Solar*
> *maxfieldso...@hotmail.com*
> * (801) 631-5584 (Cell) *
>
> --------------
> *From:* RE-wrenches on behalf
> of Dave Tedeyan
> *Sent:* Fri
Thanks Darryl,
Yea, it used to be two separate 200A services. At some point, someone
decided to turn one of those panels into a sub and run it all of a single
service.
Regarding paralleling Radians, I know that the max solar input when AC
coupled is only 6kw for an 8kw inverter. When they are paral
the 2 each 200 Amp panels is to overcome the 42 circuit limit in one
panel. must be a big house. This sounds like a whole house backup. you
will need a transfer switch much like a whole house generator switch unless
your customer needs TOU or some other grid service.
For the AC coupled parallel
Hi All,
Does anyone have a good recommendation for an AC coupled energy storage
solution for someone who has a 27.6kw array with two SE11400A-US inverters?
The output of one of those inverters is more than a Sonnen or Radian can
handle (which is what I am most familiar with).
I am not sure yet whe
5 matches