2010-02-22 Thread Mick Abraham
...that last sentence of Ray's...what a fine additional factor to bring up: Inherent current limitation because the battery just can't do more. I'm going back to my charts! Mick Abraham, Proprietor www.abrahamsolar.com Voice: 970-731-4675 On Sun, Feb 21, 2010 at 10:19 PM, R Ray Walters

Re: [RE-wrenches] single string of batts: must the interconnects be inverter size cables?

2010-02-20 Thread Doug Wells
I have always used 4/0 through out the bank. I guess that I have had to replace to many dead batteries at this point. If you are under sizing the parallel strings, what happens when a cell fails? or 2 cells fail. Now all the current would be carried by one string. If you are running equal

Re: [RE-wrenches] single string of batts: must the interconnects be inverter size cables?

2010-02-20 Thread Warren Lauzon
We usually figure that (for example) in a 2-string bank, that one conductor could carry 2/3 of the current if the batteries are unbalanced for some reason. In other words, rather than cutting the amperage rating in half, we cut it by about 1/3. For 3 banks would cut it by 1/2, etc. Probably

[RE-wrenches] single string of batts: must the interconnects be inverter size cables?

2010-02-19 Thread Mick Abraham
Example: 12 two volt battery cells in one 24 volt string. 4kW inverter/charger has 250 amp DC breaker size and 4/0 cables...as the inverter folks would want. So...do the cell to cell interconnect cables have to also be 4/0? In the example above, 2/0 interconnects would suffice from the standpoint

Re: [RE-wrenches] single string of batts: must the interconnects be inverter size cables?

2010-02-19 Thread Phil Undercuffler
The interconnects are part of the circuit. Typical flexible cables used with batteries are THW rated (75C column), so in free air 2/0 interconnects would be good for 265 amps, before any temperature derates. Therefore, you'd be safe from a NEC point of view. However, if the inverter

Re: [RE-wrenches] single string of batts: must the interconnects be inverter size cables?

2010-02-19 Thread Exeltech
As an inverter manufacturer .. I (we) agree with Phil.  He's absolutely on target with his reply. Dan Sr. Engineer --- On Fri, 2/19/10, Phil Undercuffler solarp...@gmail.com wrote: From: Phil Undercuffler solarp...@gmail.com Subject: Re: [RE-wrenches] single string of batts: must the