Re: [RE-wrenches] to flash or not to flash

2015-08-29 Thread Ray Walters
Excellent point, sir. I have looked at quite a few from the attic, later when doing upgrades, and I haven't seen leaks. But NO, I have not carefully gone back on every install to confirm. No news is good news, but that still doesn't mean 100% leak free. Also, I'm working in a drier

Re: [RE-wrenches] to flash or not to flash

2015-08-29 Thread Kurt Johnsen
To me the reports of not seeing leaks is not terribly reassuring. It’s not surprising when you consider that enough water has to get past tightly compacted shingles under an L foot, travel between the threads and the wood of a tightly threaded lag bolt, and then saturate attic insulation enough to

Re: [RE-wrenches] to flash or not to flash

2015-08-29 Thread Jerry Shafer
' re-wrenches@lists.re-wrenches.org *Sent:* Tuesday, August 25, 2015 2:19 PM *Subject:* Re: [RE-wrenches] to flash or not to flash Figured I would dig through the responses to this list topic since I posted it as a poll, of sorts. My final count was: 10 votes to flash, 4 votes not to flash

Re: [RE-wrenches] to flash or not to flash

2015-08-28 Thread Jason Szumlanski
Benn, To answer your (good) question one way, I won't speak for PV without flashings, but with literally tens of thousands of solar pool heating systems installed by all dealers that don't use flashings just in tiny Southwest Florida over the past 40 years, each system with upwards of 40

Re: [RE-wrenches] to flash or not to flash

2015-08-28 Thread Benn Kilburn
Here is a devils advocate question for everyone (*including myself*) who is claiming no leaks after x-years. Are we assuming no leaks because the home/system owner has not reported any or because there are no water stains on the ceilings below the arrays *or* are we actually looking in the attic

Re: [RE-wrenches] to flash or not to flash

2015-08-26 Thread max
From: jay jay.pe...@gmail.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Wednesday, August 26, 2015 7:44 AM Subject: [RE-wrenches] to flash or not to flash Didn’t know there was a pole. I”m on the flash side.  Question for those who don’t. How would  your insurance claim

Re: [RE-wrenches] to flash or not to flash

2015-08-26 Thread Kelly Keilwitz, Whidbey Sun Wind
Hi All, In the early days with PV and SWH we didn’t use flashings for most roofs (except tile). We used L-feet directly to the roofing with butyl (comp) or EPDM (metal) and pre-filled our holes and covered the attachments with good goop. We've never had a leak reported from this practice. And,

Re: [RE-wrenches] to flash or not to flash

2015-08-26 Thread Mike Nelson
Definitely flash, didn't do it one time, and it bit me. Michael D Nelson MD Electric Solar, Inc. 707-684-0064 mobile 707-884-1862 office www.mdelectricsolar.com Sent from my iPhone On Aug 26, 2015, at 7:44 AM, jay jay.pe...@gmail.com wrote: Didn’t know there was a pole. I”m on the flash

Re: [RE-wrenches] to flash or not to flash

2015-08-26 Thread Ray Walters
That was exactly the failure I anticipated when using flashings. Tearing up the shingle to shingle adhesive and pulling those nails out is more disruptive than the actual attachment itself. I'm going to flash on an upcoming job for legal/ insurance reasons, but not because its better. I too

[RE-wrenches] to flash or not to flash

2015-08-26 Thread jay
Didn’t know there was a pole. I”m on the flash side. Question for those who don’t. How would your insurance claim work if you didn’t flash? jay peltz power On Aug 25, 2015, at 9:59 PM, Jason Andrade ja...@westcoastsustainables.com wrote: I wouldn't install a comp roof system without

Re: [RE-wrenches] to flash or not to flash

2015-08-25 Thread Daniel Young
: Re: [RE-wrenches] to flash or not to flash Although my mind is kinda' made up, this thread has really got me thinking and researching. I scoured the NRCA manual, which does not really define penetration, but it does say in the shingle manual: Penetration Flashings: There are many small

Re: [RE-wrenches] to flash or not to flash

2015-08-25 Thread frenergy
530.284.7849 / 6544 fax solar powered since 1982 From: Daniel Young To: 'RE-wrenches' Sent: Tuesday, August 25, 2015 2:19 PM Subject: Re: [RE-wrenches] to flash or not to flash Figured I would dig through the responses to this list topic since I posted it as a poll, of sorts. My

Re: [RE-wrenches] to flash or not to flash

2015-08-10 Thread Jason Szumlanski
...@lists.re-wrenches.org] *On Behalf Of *Ray Walters *Sent:* Friday, August 07, 2015 10:34 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] to flash or not to flash My opinion is that if the L foot has enough surface area it constitutes a flashing, and that large flashings can actually cause

Re: [RE-wrenches] to flash or not to flash

2015-08-08 Thread William Dorsett
] On Behalf Of Wayne Irwin Sent: Friday, August 07, 2015 4:20 PM To: Wrenches Subject: Re: [RE-wrenches] to flash or not to flash http://www.usshingle.com/wp-content/uploads/2013/08/US-Shingle-Roof-Tune-Up .png http://www.usshingle.com/wp-content/uploads/2013/08/US-Shingle-Roof-Tune-Up. png

Re: [RE-wrenches] to flash or not to flash

2015-08-08 Thread jerrysgarage01
@lists.re-wrenches.org> Subject: Re: [RE-wrenches] to flash or not to flash I agree with Ray on this, but think the neoprene boot here is so badly separated more likely because the house is settling around it. Still it cracked due to UV and would have failed anyway.Bill DorsettManhattan, KSFrom:

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Jason Szumlanski
-wrenches *Subject:* Re: [RE-wrenches] to flash or not to flash My opinion is that if the L foot has enough surface area it constitutes a flashing, and that large flashings can actually cause more damage to the roof than they prevent. I also agree that an attachement doesn't constitute

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Ray Walters
We did a shake roof, and used a quick mount flashing ( I believe) that was 18 x 18. According to the directions, we had to use a roofing bar to pull out the nails to insert the flashing up under the shake. Missing nails the shakes were not secure on the neds, so we ended up using sealant to

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread David Brearley
It may be helpful to distinguish between exposed-fastener metal roofs and other roofing systems. If you’re working on a metal roof that is attached with exposed fasteners, I don’t know of any practical solution for retrofitting PV without adding more exposed fasteners. And, yes, the mastic

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Jason Szumlanski
...@lists.re-wrenches.org] *On Behalf Of *Ray Walters *Sent:* Friday, August 07, 2015 10:34 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] to flash or not to flash My opinion is that if the L foot has enough surface area it constitutes a flashing, and that large flashings can actually

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Ray Walters
Hi William; First, a sealed L foot is not a sealant only attachment system. It has quite a bit of surface area beyond the hole just like a flashing, and has mechanical attachment through the roof to the structure (which a flashing often does not). I consider an L foot to be a mini flashing

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Ray Walters
My opinion is that if the L foot has enough surface area it constitutes a flashing, and that large flashings can actually cause more damage to the roof than they prevent. I also agree that an attachement doesn't constitute a penetration. I just finished an install on a metal roof with hundreds

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread William Miller
Gradient Cap_mini Lic 773985 http://www.millersolar.com/ millersolar.com 805-438-5600 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters Sent: Friday, August 07, 2015 10:34 AM To: RE-wrenches Subject: Re: [RE-wrenches] to flash or not to flash My

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Jay
Hi Ray Can you elaborate on how a large flashing can cause more damage than it prevents? Thanks Jay Peltz power Sent from my iPhone On Aug 7, 2015, at 10:34 AM, Ray Walters r...@solarray.com wrote: My opinion is that if the L foot has enough surface area it constitutes a flashing,

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Wayne Irwin
this message from your computer system. Thank you. Date: Fri, 7 Aug 2015 17:11:50 -0400 From: kjenergysyst...@gmail.com To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] to flash or not to flash Not that the names of things matter that much but imho flashing does require an overlapping

Re: [RE-wrenches] to flash or not to flash

2015-08-07 Thread Kurt Johnsen
-5600 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters *Sent:* Friday, August 07, 2015 10:34 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] to flash or not to flash My opinion is that if the L foot has enough surface area it constitutes

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread William Miller
Daniel: Good question, and worthy of revisiting. As a contractor and businessman, I am obligated to reduce risk exposure by using best evolved practices. This requires I used modern, purpose-built, approved attachment hardware. To my knowledge, these are all flashed. No roofing contractor

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Conrad Geyser
-wrenches.org, Date: 08/06/2015 10:16 AM Subject: Re: [RE-wrenches] to flash or not to flash Sent by: RE-wrenches re-wrenches-boun...@lists.re-wrenches.org -- Daniel, My answer is to flash until others prove me wrong. I am in the same position you are, speaking

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Conrad Geyser
Hi fellow Wrenches, Flashing - We have ~30 years experience with ~700 systems dating back to 1980 here in the Northeast primarily on asphalt shingles. Standard attachment method on these historic systems and currently for us is a lagged foot bedded in silicone. We've seen no leaks including

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread penobscotsolar
, BC V5G4M1 *** Please consider the environment before printing this e-mail From: Matt Partymiller m...@solar-energy-solutions.com To: RE-wrenches re-wrenches@lists.re-wrenches.org, Date: 08/06/2015 10:16 AM Subject: Re: [RE-wrenches] to flash or not to flash Sent by: RE

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Tump
As NABCEP certified installers, the signed agreement states that; we as Pros will use the IBC and other applicable codes for design installation methods. I will say that I loose jobs due to the additional cost of components labor to install flashings. It is very frustrating having my local

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Matt Partymiller
Daniel, My answer is to flash until others prove me wrong. I am in the same position you are, speaking to the same manufacturers you are, and probably dealing with the same low competitor pricing you are. These products sure sound tempting. Over the past decade I have probably removed a dozen

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Jason Szumlanski
40+ years of experience from the solar pool industry shows that shingle roof attachments without flashing with proper sealant and methods can be very successful. Typical pool heating systems involve 50+ attachments done without flashing. BUT, that experience is primarily based on two things that

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Jarmo . Venalainen
m...@solar-energy-solutions.com To: RE-wrenches re-wrenches@lists.re-wrenches.org, Date: 08/06/2015 10:16 AM Subject: Re: [RE-wrenches] to flash or not to flash Sent by: RE-wrenches re-wrenches-boun...@lists.re-wrenches.org Daniel, My answer is to flash until others prove me wrong. I am

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Tump
: www.Xantrex.com | Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 Mail Attachment.gif From: Matt Partymiller m...@solar-energy-solutions.com To: RE-wrenches re-wrenches@lists.re-wrenches.org, Date: 08/06/2015 10:16 AM Subject: Re: [RE-wrenches] to flash or not to flash Sent

[RE-wrenches] to flash or not to flash

2015-08-06 Thread Daniel Young
Writing the subject above, it seems like I've heard this question on the wrench list before, but I could not find it in my old email archives. Feel free to pint me back to the old discussion if it's there. I've been using a flashing based roof attachment for 8+yrs now (quick mount or similar).

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Jason Szumlanski
-wrenches.org, Date: 08/06/2015 10:16 AM Subject: Re: [RE-wrenches] to flash or not to flash Sent by: RE-wrenches re-wrenches-boun...@lists.re-wrenches.org -- Daniel, My answer is to flash until others prove me wrong. I am in the same position you are, speaking

Re: [RE-wrenches] to flash or not to flash

2015-08-06 Thread Glenn Burt
'smart' phone so please excuse grammar and typos. -Original Message- From: jarmo.venalai...@schneider-electric.com jarmo.venalai...@schneider-electric.com Sent: ‎8/‎6/‎2015 13:34 To: RE-wrenches re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] to flash or not to flash Hi