True and thank you for clarifying that; however, the examples I cited
are all only applicable to NFPA 13 systems in the 2006 edition we
enforce if the table I referred to is accurate.
The table I used is Figure 903.3.1.1(2), "Examples of Requirements
Modified Through Use of Automatic Sprinkler S
slow down on the full 13 requirement for trade-offs since that started
changing a few cycles ago. In R occupancies, many trade-offs can be
applied with a 13R system. Also careful on "provided throughout"
since that does not mean every area of the building since even 13 has
some areas with
You're correct Ron. Biggest reasons for not sprinklering is either fear of
accidental head discharge and/or electrocution from the accidental head
discharge. Neither can be substantiated through verifiable statistics.
Last year I did some investigation of reported Industrial accidents related
If you are in a market that uses PEX on the plumbing side you should be able to
purchase a PEX x PB coupling crimp x crimp as well as the crimp tool required
from most plumbing supply houses. Please note that this assembly is not a
listed assembly however, it will do the job (as long as the stat
Remember that the Architect may not want to use the exception for 13R or
13D in I-1 if he needs to retain the "fully sprinklered per NFPA 13"
status that he made need for many IBC code exceptions/modifications such
as the allowable building area increase [506.3], rating reductions
[508.3.3, Table 6
Addressing Craig's mention of perceptions. There is a horrendous fear
of water damage among most (and especially electrical) engineers. I
once had an electrical engineer tell me you couldn't sprinkler a
hydro-electric plant. First because it was too full of electrical
equipment and secondly (and mo
It makes no difference whether the line passes through the room or comes in and
stops as long as you are in the allowable space as defined within the section
of the electrical code. People are extrapolating limitations based on their
perception not on code verbiage. We've had several detailed
Is it portraying an electrical room or an electrical vault?
Roland
On Jan 5, 2010, at 6:43 AM, cowprop...@aol.com wrote:
> In the handbook of NFPA 72 they show a figure where the sprinkler pipe
> ends in the electrical room , but it does not go thru the room.
> mario berrios
>
>
> -Original
In the handbook of NFPA 72 they show a figure where the sprinkler pipe
ends in the electrical room , but it does not go thru the room.
mario berrios
-Original Message-
From: George Church
To: sprinklerforum@firesprinkler.org
Sent: Mon, Jan 4, 2010 11:54 am
Subject: RE: Electrical Rooms
Here's the report.
http://www.scribd.com/doc/24417667/Riverview-Report
At 02:45 PM 1/4/2010, you wrote:
>George,
>
>I think this is the fire you're discussing from Wells, NY. Here's the
>information from the Albany Times-Union on Dec 23.
>
>http://www.timesunion.com/AspStories/story.asp?storyI