RE: Group 'I' Occupancies

2010-01-05 Thread David Blackwell
True and thank you for clarifying that; however, the examples I cited are all only applicable to NFPA 13 systems in the 2006 edition we enforce if the table I referred to is accurate. The table I used is Figure 903.3.1.1(2), "Examples of Requirements Modified Through Use of Automatic Sprinkler S

Re: Group 'I' Occupancies

2010-01-05 Thread Roland Huggins
slow down on the full 13 requirement for trade-offs since that started changing a few cycles ago. In R occupancies, many trade-offs can be applied with a 13R system. Also careful on "provided throughout" since that does not mean every area of the building since even 13 has some areas with

RE: Electrical Rooms

2010-01-05 Thread Craig.Prahl
You're correct Ron. Biggest reasons for not sprinklering is either fear of accidental head discharge and/or electrocution from the accidental head discharge. Neither can be substantiated through verifiable statistics. Last year I did some investigation of reported Industrial accidents related

Re: PB (Polybutylene) Pipe

2010-01-05 Thread Mike Cabral
If you are in a market that uses PEX on the plumbing side you should be able to purchase a PEX x PB coupling crimp x crimp as well as the crimp tool required from most plumbing supply houses. Please note that this assembly is not a listed assembly however, it will do the job (as long as the stat

RE: Group 'I' Occupancies

2010-01-05 Thread David Blackwell
Remember that the Architect may not want to use the exception for 13R or 13D in I-1 if he needs to retain the "fully sprinklered per NFPA 13" status that he made need for many IBC code exceptions/modifications such as the allowable building area increase [506.3], rating reductions [508.3.3, Table 6

Re: Electrical Rooms

2010-01-05 Thread Ron Greenman
Addressing Craig's mention of perceptions. There is a horrendous fear of water damage among most (and especially electrical) engineers. I once had an electrical engineer tell me you couldn't sprinkler a hydro-electric plant. First because it was too full of electrical equipment and secondly (and mo

RE: Electrical Rooms

2010-01-05 Thread Craig.Prahl
It makes no difference whether the line passes through the room or comes in and stops as long as you are in the allowable space as defined within the section of the electrical code. People are extrapolating limitations based on their perception not on code verbiage. We've had several detailed

Re: Electrical Rooms

2010-01-05 Thread Roland Huggins
Is it portraying an electrical room or an electrical vault? Roland On Jan 5, 2010, at 6:43 AM, cowprop...@aol.com wrote: > In the handbook of NFPA 72 they show a figure where the sprinkler pipe > ends in the electrical room , but it does not go thru the room. > mario berrios > > > -Original

Re: Electrical Rooms

2010-01-05 Thread cowprophet
In the handbook of NFPA 72 they show a figure where the sprinkler pipe ends in the electrical room , but it does not go thru the room. mario berrios -Original Message- From: George Church To: sprinklerforum@firesprinkler.org Sent: Mon, Jan 4, 2010 11:54 am Subject: RE: Electrical Rooms

Re: Group 'I' Occupancies

2010-01-05 Thread Todd Williams
Here's the report. http://www.scribd.com/doc/24417667/Riverview-Report At 02:45 PM 1/4/2010, you wrote: >George, > >I think this is the fire you're discussing from Wells, NY. Here's the >information from the Albany Times-Union on Dec 23. > >http://www.timesunion.com/AspStories/story.asp?storyI