Well I'll be go to hell, I finally got a gold star from Teach
> On Mar 5, 2014, at 10:19 PM, "rongreenman ." wrote:
>
> Good boy, Brad.
>
> No numbers, just code.
>
>
> On Wed, Mar 5, 2014 at 8:11 PM, Brad Casterline
> wrote:
>
>> So, based on my definition of a Standard, if the stockpile o
Good boy, Brad.
No numbers, just code.
On Wed, Mar 5, 2014 at 8:11 PM, Brad Casterline wrote:
> So, based on my definition of a Standard, if the stockpile of combustibles
> does not exceed 8 feet, I would submit Light Hazard, and let the chips fall
> where they may.
>
> > On Mar 5, 2014, at 9:4
So, based on my definition of a Standard, if the stockpile of combustibles does
not exceed 8 feet, I would submit Light Hazard, and let the chips fall where
they may.
> On Mar 5, 2014, at 9:46 PM, Todd Williams wrote:
>
> If it is Rankine or Kelvin, it has already gone off.
>
>
> Todd G Wil
If it is Rankine or Kelvin, it has already gone off.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com
> On Mar 5, 2014, at 9:13 PM, John Denhardt
> wrote:
>
> Is that Fahrenheit or Celsius?
>
> Or for the Terps types - Rankine or Kelvin.
>
>
When I worked for FE Moran, Special Hazards Div. this was standard
procedure.
On 3/5/2014 12:27 PM, Richard Mote wrote:
Use to do it all the time, "Automatic" used to make a standard spray pendent
and upright with a glass strut thru a metal tag with a hole in it. After we pressure
tested
This is a no-brainier Craig:
>From NFPA 13 (any modern edition, 5.2 and 5.3, if the quantity and/or
>combustibility of the contents is low and fires with relatively low rates of
>heat release are expected, it is L.H.
If the combustibility is low, quantity of combustibles is moderate, stockpiles
Is that Fahrenheit or Celsius?
Or for the Terps types - Rankine or Kelvin.
Thanks,
John August Denhardt P.E.
> On Mar 5, 2014, at 9:09 PM, "rongreenman ." wrote:
>
> So many things to say:
>
> It's he TEA Party head.
>
> I interpolated a temperature.
>
> If Suzy has a 286 degree head and s
So many things to say:
It's he TEA Party head.
I interpolated a temperature.
If Suzy has a 286 degree head and she gives 30 degrees to Billy how many
degrees does she have left?
Let your fingers do the stumbling.
Roland wrote that.
On Wed, Mar 5, 2014 at 5:42 PM, Todd Williams wrote:
> 256
256 degree head? Is that a 286 degree head after budget cuts?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com
> On Mar 5, 2014, at 8:34 PM, "rongreenman ." wrote:
>
> Depends. What's the rest of the building? If in a residence then What
> abou
Depends. What's the rest of the building? If in a residence then What
about in a hotel versus in a gym. Dry sauna is a lot like a mini fur vault.
Wet sauna more like a swimming pool or hot tub room. The biggest danger
statistically is people getting hurt slipping and falling, after an
unwanted
I would probably consider it OH1 but the ones I'm used wouldn't require more
than 1 or 2 sprinklers so I never got too concerned about it
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
> On Mar 5, 2014, at 7:06 PM, "Craig Leadbetter"
> wrot
What hazard would you classify a Sauna? Light or Ordinary Hazard?
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855
(P) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393
___
Sprinklerforum mailing list
Sprinklerforum@lists.fir
Anyone ever installed ESFR sprinklers under solid catwalks. I know 8.12.5
addresses the issue. Is it considered a in rack sprinkler? Is it fed from a
separate riser, and does it have to be balanced with the overhead system?
Jay White
Dynamic Fire Protection
9771 Highway 25 South
Starkville,
Use to do it all the time, "Automatic" used to make a standard spray pendent
and upright with a glass strut thru a metal tag with a hole in it. After we
pressure tested you could walk through the job with a long pole with a hook on
it and pull out the struts.
Richard L. Mote
Rowe Sprinkler Sys
OK, thanks for all the input.
We will now return to our regularly scheduled program...
Craig L. Prahl, CET
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension
Standard practice in many cases. You use standard spray which aren't listed
for a particular application. What would you use in an EH that just
required sprinklers? If I can get the a system to calc through 1/2" closed
sprinklers at the necessary density I can use them. What's the difference?
In so
Agree - It is the way I have been taught to do it.
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rfletc...@aerofire.com
Sent: Wednesday, March 05, 2014 9:57 AM
To: sprinklerforum@lists.firespri
It's done all the time. Do the hydro test then knock out the links.
Ron F
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, March 05, 2014 7:25 AM
To: sprinkle
Received a shop drawing stating that for the deluge system, the contractor
would purchase standard fused sprinklers and remove the fusible link.
Now I can't find specific NFPA verbiage that would prohibit this but seems to
me that a sprinkler that is listed for LH or OH occupancies would not be