RE: Class I standpipe - high pressure zone

2016-03-24 Thread Steve Leyton
Just saw this ... DeWayne, we recently did a 500 foot tall building with a single zone. I'm not sure what your specifying engineer is thinking, but the cost of fire protecting this building went way, way up when he made the decision to specify two zones. Steve Original message -

RE: Class I standpipe - high pressure zone

2016-03-24 Thread Steve Leyton
Assuming your high zone FDCS are tied to the common feed mean that supplies the two guys on risers, you do not need a second interconnection. Or at least that's my best guess, without seeing a plan or knowing exactly how high the building is. My opinion only, Steve Original message

RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Larry Keeping
Just a bit of an update: Per NFPA24-2016 & NFPA 13-2016, Section 10.1.4.1 10.1.4.1 Underground piping shall be permitted to extend into the building through the slab or wall not more than 24 in. (600mm). A.10.1.4.1 Where nonmetallic underground piping is provided a

RE: Class I standpipe - high pressure zone

2016-03-24 Thread Dewayne Martinez
There are separate fire department connections for the low and high pressure zones. There is a common supply for the high pressure zone in the basement which feeds two vertical risers each individually controlled by butterfly valves. What I am asking is if these two feeds must be looped together

RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Craig.Prahl
The problem with PVC or any non-metallic pipe is that if they are not listed for above ground service you may need to transition from the plastic to a metallic pipe above the slab. Check the manufacturer's listing for installation restrictions. At fire temperatures the plastic could be structur

RE: Class I standpipe - high pressure zone

2016-03-24 Thread Dewayne Martinez
Yes, The top floor is 370ft above grade. The specifying engineer requested two zones on the bid documents. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Thursday, March 24, 2016 10:04 AM To: sprinklerforum

RE: High-Speed and Ultra-High Speed Deluge Systems

2016-03-24 Thread Craig.Prahl
Pyrotech and Pilotex (Pilotex was SimplexGrinnell) are the two main stream suppliers of these systems I've used. Very specialized applications with complex designs and are typically big ticket items. Craig L. Prahl Fire Protection Group Lead/SME CH2MHILL Lockwood Greene 1500 International

Re: ESFR & Smoke Vents

2016-03-24 Thread Ron Fletcher
Depends on the egress distance also. If 400 ft is used rather than 250 ft. Then smoke vents are required. Sent from my iPhone > On Mar 24, 2016, at 12:09 PM, Reed A. Roisum, SET > wrote: > > I don't know of that requirement. > > Section 910 of the IFC says "where installed in buildings equip

Re: High-Speed and Ultra-High Speed Deluge Systems

2016-03-24 Thread Ron Fletcher
If you want to contact me off forum I can get you in touch with two companies that do HSD. I did a bunch of it back during the mid to late 90's. Ron Fletcher FP Specialists, LLC fpspecial...@yahoo.com Sent from my iPhone > On Mar 24, 2016, at 12:21 PM, Reed A. Roisum, SET > wrote: > > Chris,

RE: High-Speed and Ultra-High Speed Deluge Systems

2016-03-24 Thread Reed A. Roisum, SET
Chris, Have you looked at Pyrotech? http://pyrotechusa.com/ What is the application? Explosion protection? Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -

RE: ESFR & Smoke Vents

2016-03-24 Thread Reed A. Roisum, SET
I don't know of that requirement. Section 910 of the IFC says "where installed in buildings equipped with an approved automatic sprinkler system, smoke and heat vents shall be designed to operate automatically." The commentary explains that the fusible link temperature should be coordinated wi

Re: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Parsley Consulting
Cesar, If I read your inquiry correctly the data you need is most likely in FM Global Data Sheet 3-10, in Table 1. It looks as though they don't make a distinction in that data sheet based on the type of occupancy. *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *E

RE: ESFR & Smoke Vents

2016-03-24 Thread John Paulsen
Brian: Try NFPA-13, 2013, section 12.1.1. The concern is that the vents operate AFTER the ESFR sprinklers and don't delay their activiation. John Paulsen - SET Crown Fire System Design 6282 Seeds Rd. Grove City, OH 43123 P - 614-782-2438 F - 614-782-2374 C - 614-348-8206 -Original Mess

Re: ESFR & Smoke Vents

2016-03-24 Thread Bobby Gillett
NFPA13-2013 12.1.4.1 (4) Bobby Gillett *Living Water Fire Protection, LLC* 1160 McKenzie Rd. Cantonment, FL 32533 (850) 937-1850 On Thu, Mar 24, 2016 at 10:07 AM, Brian Harris wrote: > I recall reading somewhere that if you're using ESFR heads and there are > roof vents present they need to be

ESFR & Smoke Vents

2016-03-24 Thread Brian Harris
I recall reading somewhere that if you're using ESFR heads and there are roof vents present they need to be monitored and closed if there's an activation, correct? Can anybody tell me where I saw that :) Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com

RE: Class I standpipe - high pressure zone

2016-03-24 Thread Steve Leyton
How will the fire department connections be configured if the standpipes aren't interconnected? Steve Original message From: Dewayne Martinez Date: 3/24/2016 8:20 AM (GMT-07:00) To: sprinklerforum@lists.firesprinkler.org Subject: Class I standpipe - high pressure zone NFPA

RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Reed A. Roisum, SET
Cesar, All I could find was in FMDS 3-10... 2.1.2. Fire Service Mains 2.1.2.1 General 2.1.2.1.1 Use Approved underground pipe, joints and fittings for fire service mains. Acceptance of pipe, joints and fittings that are not Approved is based on satisfactory experience and conformity to specific

Re: Class I standpipe - high pressure zone

2016-03-24 Thread Roland Huggins
are you in a tall enough building where you actually have upper and a lower pressure zones? Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org > On Mar 24, 2016, a

Class I standpipe - high pressure zone

2016-03-24 Thread Dewayne Martinez
NFPA 14 - 07ed Looking at figure A7.1(b) for a two zone system it shows the high pressure zone standpipe feeds interconnected. Is this required? I have two stairwells for the upper tower area and it would be nice to keep the feeds in the stairwells without having to run 6in across the building