Re: Sloped Roof in ESFR system

2017-05-10 Thread Bruce Verhei
From 3 lbs/sf : 24 lbs/typ 2' x 4' tile. Does architect have a clue that vertical jet at ceiling is measured in tens of mph, not lf/m or inches of pressure as are commonly used in HVAC? Is the fire plan reviewer skookum enough to ask what design standard was used or for a rational design analy

Re: Automated storage machine

2017-05-10 Thread Bruce Verhei
Have you talked directly with the pick system designing firms? In the case of the totes with slots I'd expect them to provide a technical report by competent persons that analyzes the fire protection methodology. In the case of the original question, does the manufacturer provide an option A wi

Re: Sloped Roof in ESFR system

2017-05-10 Thread Roland Huggins
Pete I thought something was submitted or the 2019 addressing ceiling weight and restricting upwards lift. Ring any bells? Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org Fire Sprinklers Saves

RE: Automated storage machine

2017-05-10 Thread Steve Leyton
Are you referring to 8-33 as noted earlier in the thread? That includes retrieval systems. Has anyone seen a system called Perfect Pick™ as manufactured by Opex Corporation? Let me add to the confusion … this one is a really big (30’ high and up to 225’ long) double aisle columnar system th

RE: Automated storage machine - Character set not allowed

2017-05-10 Thread Mark Phillips
Yes Sir Coverage at the top with pendents through roof Run pipe down the outside and sidewall heads spaced vertically From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise Sent: Wednesday, May 10, 2017 2:04 PM To: sprinklerforum@lists.firesprinkler

RE: Automated storage machine

2017-05-10 Thread Jim Davidson
Matt, Factory Mutual has done testing in such storage units and and has published a data sheet on the protection of such units. I forget which FM Data Sheet that addresses the storage units but the protection guide lines are very specific and detailed. Good luck. Have a fire safe day! Jim Da

RE: Automated storage machine

2017-05-10 Thread Mitchell, Scott
We installed a sprinkler at the top, selecting a concealed type to ensure it didn’t get wacked by internal moving parts. J. Scott Mitchell, PE Senior Fire Protection Engineer Mission Engineering CNS Y-12 | 865-576-5258 CNS PTX | 806-477-5883 From: Sprinklerforum [mailto:sprinklerforum-boun...@li

RE: Automated storage machine

2017-05-10 Thread Mike Stossel
Yes, a protected a vertical carousel. I used FM data sheet 8-33 for guidance. Mike Stossel SET [400dpiLogoCropped] 36 Barren Road East Stroudsburg, PA 18302 Office: 973-670-2627 m...@knssprinkler.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firespri

Automated storage machine

2017-05-10 Thread Matt Grise
I am looking at protecting the interior of an automated storage machine. It has lots of small bins in it and you type what you want into a keypad it brings that bin down to an access area so you can grab what you need. The machine is 30 or so feet tall and is designed to take the place of severa

RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
I started in FM data sheet 2-0 section 2.2.1.6 ceiling slope. This directs you to the definition of a false ceiling in appendix A and Data Sheet 1-12. Appendix A says that a suitable ceiling would be 3/8” plywood or gypsum board or you could also use corrugated or sheet metal. It also directs

RE: Sloped Roof in ESFR system

2017-05-10 Thread Matt Grise
I am not able to find that in my copy of 1-12. Can you direct me to a section? I downloaded the May 2008 edition. Thanks! Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Stossel Sent: Wednesday, May 10, 2017 9:14 AM To: sprinklerforum@lists.

RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
Data sheet 1-12, they say that the ceiling construction needs to withstand a minimum uplift pressure of 3 lb/ft². Mike Stossel SET [400dpiLogoCropped] 36 Barren Road East Stroudsburg, PA 18302 Office: 973-670-2627 m...@knssprinkler.com From: Sprinklerforum [mailto:s

RE: Sloped Roof in ESFR system

2017-05-10 Thread Matt Grise
What FM guidelines are you using? I had a project come up that used a drop ceiling in a storage location and I had a difficult time finding guidelines for ceiling construction. Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Stossel Sent: We

RE: RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
They didn’t say, but I will be recommending it if they decide on the acoustical ceiling. Mike Stossel SET [400dpiLogoCropped] 36 Barren Road East Stroudsburg, PA 18302 Office: 973-670-2627 m...@knssprinkler.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lis

Re: RE: Sloped Roof in ESFR system

2017-05-10 Thread fpdcdesign
Clips on the ceiling tiles? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-553-3553 (tel:860-553-3553) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On May 10, 2017 at 9:47 AM

RE: Sloped Roof in ESFR system

2017-05-10 Thread Byron Weisz
I guess just me but I would never design an unused attic space above a 30’-0 flat ceiling to Light Hazard. Especially in a warehouse where there is going to be rack storage below. [ccfs_LOGO (2)] Byron Weisz Cen-Cal Fire Systems, Inc. P.O. Box 1284 Lodi, CA 95241 Phone (209) 334-9119 Fax (

RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
I agree. I am trying to get them to follow FM’s guidelines for the ceiling construction, but they currently have an architect saying that an acoustical ceiling will be adequate. Since FM’s way will be more expensive, and the architect is approving it, the owner will most likely be going with t

RE: Sloped Roof in ESFR system

2017-05-10 Thread Pete Schwab
My concern would be what is the ceiling constructed of. If it is an acoustical tile ceiling with no clips I would be concerned with the velocity of the fire plume popping tiles before operating a sprinkler. Peter Schwab VP of Purchasing and Engineering technologies Wayne Automatic Fire Sprinkle

Re: Sloped Roof in ESFR system

2017-05-10 Thread John Denhardt
Confirmed - light hazard. John August Denhardt, P.E. Strickland Fire Protection On May 10, 2017, at 7:13 AM, Richard Carr mailto:rc...@coxfire.com>> wrote: Yes, unused attic is light hazard but you are limited on head spacing. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grac

RE: Sloped Roof in ESFR system

2017-05-10 Thread Clifford Whitfield
Mike, It sounds like LH but you will need to refer to Table 8.6.2.2.1(a) for spacing requirements. (2010 ed) Cliff Whitfield, SET President Fire Design, Inc. 184 Comfort Place Burnsville, NC 28714 Ph: 828-284-4772 [Description: New FDI Logo-4.jpg] cl...@fire-design.com

RE: Sloped Roof in ESFR system

2017-05-10 Thread Richard Carr
Yes, unused attic is light hazard but you are limited on head spacing. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 rc...@coxfire.com 904-781-8227 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike

Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
I am currently working on an old wood building that my client wants to use for rack storage. The building has a sloped roof that exceeds the allowable pitch so they will be installing a dropped ceiling to create the flat surface. The area above the ceiling will now be a combustible concealed s