Ames will sell you a preassembled backflow with a PIV valve.  It just adds a 
lead time to the order.



-----Original Message-----
From: Steve Leyton <st...@protectiondesign.com>
To: sprinklerforum@lists.firesprinkler.org 
<sprinklerforum@lists.firesprinkler.org>
Sent: Tue, Dec 4, 2018 5:50 pm
Subject: RE: [EXTERNAL] Re: RE: PIV



Yeah, they’re exactly the same valve guts and exactly the same take-out and 
exactly the same everything-else-functionally but if you swap the factory 
assembled valve out for another one the USC approval goes “POOF!”.    That’s 
why my question yesterday was whether anyone knew of a device that was sold new 
with a PIV gate valve … from the factory.   They are listed exactly as they are 
tested, which is very time-consuming and expensive.   USC tests entail pressure 
testing (forward and backward) and a one-year continuous service test and they 
have to fully test both butterfly and gate valve versions.  Not sure if it’s 
required to separately test all the possible combinations of shut-off valves 
and horizontal, vertical, “N” and “Z” patterns.
 
  
 
Steve L.
 
  
 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]On 
Behalf Of Pete Schwab
Sent: Tuesday, December 04, 2018 5:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: RE: PIV
 

  
 
Ron,
 
That would be acceptable unless the water purveyor requires a USC approved 
device. I don’t believe that arrangement has been through USC
 
  
 
Peter Schwab
 
VP of Purchasing and Engineering technologies
 
  
 
Wayne Automatic Fire Sprinklers Inc.
 
222 Capitol Court
 
Ocoee, Fl 34761
 
  
 
Mobile: (407) 468-8248
 
Direct: (407) 877-5570
 
Fax: (407) 656-8026
 
  
 
www.waynefire.com
 
  
 
 
  
 
 
  
 
I sleep in a sprinklered home, do you?
 
  
 
  
 
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>On Behalf 
Of Ron Greenman
Sent: Monday, December 3, 2018 7:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] Re: RE: PIV
 
  
 
I once took a look at a Kennedy OS&Y, an NRS, they type where you use the 2" 
square key to operate and a yard PIV. The main valve body and the discs were 
the same part number in all cases. The difference had to do with whether it was 
a gland or stuffing box bonnet, and the parts used in the operating mechanism. 
In the case of the square nut gate valve the only difference was the post parts 
themselves. At yet...

 





  
 

  
 

Ron Greenman
 

rongreen...@gmail.com

253.576.9700
 

  
 

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
 





  
 
  
 

On Mon, Dec 3, 2018 at 2:45 PM Pete Schwab <pe...@waynefire.com> wrote:
 

Steve
 
I have never seen one.
 
Pete
 
 
 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>On Behalf 
Of Steve Leyton
Sent: Monday, December 3, 2018 5:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: RE: PIV
 

 
 
Any suppliers or others on this thread that know if a backflow appliance can be 
ordered with a listed PIV on the owner’s side?
 
 
 
Steve
 
 
 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]On 
Behalf Of Prahl, Craig/GVL
Sent: Monday, December 03, 2018 2:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: RE: PIV
 

 
 
Typically the reason is both, (1) to be able to control sprinkler flow from 
outside the bldg. and (2) to verify that the water supply is available.
 
 
 
I can’t speak to whether or not the non-indicating valve should be removed, 
that would be a decision by the AHJ.  But its presence in the system creates 
risk if it is not inspected daily to ensure it is always in the open position.
 
 
 
Craig Prahl|Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com| www.jacobs.com
 
 
 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>On Behalf 
Of Kyle.Montgomery
Sent: Monday, December 03, 2018 4:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: RE: PIV
 

 
 
So, in that case, would they be required to eliminate the non-indicating gate 
valve? Or just add the PIV? I mean, if the gate valve is closed, it really 
doesn’t matter what position the PIV is in.
 
 
 
I know there are some jurisdictions in Nevada where we’ve been required to 
provide wall PIVs for the system control valves. But I’m not 100% certain what 
their intent was in requiring it. Is it about knowing if the valve is open or 
closed, or is it about being able to control it from the building exterior?
 
 
 
-Kyle M
 
 
 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]On 
Behalf Of Prahl, Craig/GVL
Sent: Monday, December 3, 2018 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: RE: PIV
 

 
 
NFPA 24 calls for indicating type valves on water supplies serving sprinklers.  
Non-indicating type valves for sprinkler water control are permitted only when 
approved by the AHJ.  So it’s totally within the right of the AHJ to require a 
PIV outside the room on the UG run-in.
 
 
 
In some cases when there is no place to install a PIV, sometimes the AHJ has 
allowed a Wall Post Indicator Valve to be used.
 
 
 
Craig Prahl|Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com| www.jacobs.com
 
 
 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>On Behalf 
Of Bruce Verhei
Sent: Monday, December 03, 2018 3:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Re: RE: 
 

 
 
To follow JD’s comment, new or existing would to me be the big question.  Or 
said another way, if new, why weren’t approved plans followed? 
 
 
 

Best.
 

 
 

Bruce Verhei 
 

On Dec 3, 2018, at 12:10, Matt Grise <m...@afpsprink.com> wrote:
 

There is a city we work in where every building must have a PIV. I don’t know 
if that is in the code, but the fire department won’t approve a system without 
one.
 
 
 
Matt
 
 
 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>On Behalf 
Of Randy Huffman
Sent: Monday, December 03, 2018 2:06 PM
To: Sprinklerforum@lists.firesprinkler.org
Subject: 
 

 
 
We have a riser room at the rear of a building. An exterior door opens to 
interior of riser room which contains a backflow preventer with two indicating 
control valves, a rise check valve, and a water flow switch. Underground line 
to building has a nonindicating gate valve in roadway box some distance from 
door to riser room. AJH says a post indicator valve must be installed outside 
riser room. We believe the current arrangement of piping and valves meets the 
standard without the PIV
 
Please comment.
 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 

 
 
------------------------------------------------------------


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
 
 
 
------------------------------------------------------------


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to